M1804.2.3 Natural draft appliances.
Vents for natural
draft
appliances shall terminate at least 5 feet (1524 mm)
above the highest connected appliance outlet,
I also saw somewhere in the IRC that the B vent must extend a minimum of 1 foot above a sloped roof.
My question is: What if a waterheater is located on a verticle wall 10 feet high. Is the vent to extend 5 feet or 11 feet?
Thank you.
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-16-2009, 09:48 PM #2
Re: Clarification on vent termination
Depends on how tall the water heater is.

-
12-16-2009, 10:04 PM #3
Re: Clarification on vent termination
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
12-16-2009, 10:27 PM #4
Re: Clarification on vent termination
Marc was thinking floor to ceiling height was 10 feet plus 1 foot above the roof would give an 11 foot vent.
But the vent connection of the water heater is not at the floor. Typically about 5 feet above the floor which would give a 6 foot long vent. Six feet is ok since 6 feet is "at least 5 feet (1524 mm)
above the highest connected appliance outlet".
-
12-16-2009, 10:38 PM #5
Re: Clarification on vent termination
Is the b-vent connected directly to the appliance or draft hood probably not.
You have a vent connector likely SW then at least a 12" vertical rise before any offset then the bvent.
What's your roof material and pitch or slope you'll have to exceed the highest surface in a radius area by a distance certain and note any nearby projections, walls, other which affect the exhaust/draft.
Is California using the IRC Mechanical chapters now?
You might find NFPA 211 helpful its the AGA/ANSI standard that the manufacturer's of the gas fired water heaters refer to most often in their instructions.
-
12-16-2009, 10:39 PM #6
Re: Clarification on vent termination
Marc,
For a gas fired appliance, terminations of B and BW vent need to terminate 1' above roof with a roof pitch up to 6/12. If the vent is closer than 8' to a vertical wall then the vent termination must terminate 2' above roof edge. So the vent at your water heater must extend to 12'.
-
12-16-2009, 10:49 PM #7
Re: Clarification on vent termination
Ohhh... I get it. I guess I am a little slow today (just today?)
The termination would need to be above the roof. I seem to recall that a B-vent within 8 feet of a vertical wall must be 2 feet above.
2006 IRC: 2427.6.4
2006 UMC: 806.6.2
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
12-16-2009, 10:51 PM #8
Re: Clarification on vent termination
Oh, geeze... too slow on the draw again. But at least, I supplied the sections.

Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
12-16-2009, 10:53 PM #9
Re: Clarification on vent termination
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
12-16-2009, 11:38 PM #10
Re: Clarification on vent termination
Last edited by Marc M; 12-16-2009 at 11:45 PM.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-16-2009, 11:43 PM #11
Re: Clarification on vent termination
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-17-2009, 02:11 PM #12
Re: Clarification on vent termination
Oops NFPA 54 - call it a sr. moment.
-
12-17-2009, 05:28 PM #13
Re: Clarification on vent termination
Actually, I had not noticed that. Thanks.
Sorry, typed the UMC section number incorrectly. Presumably, they still require the minimum height above the roof noted in the tables that you mentioned.
802.6.2.3 A gas vent extending through an
exterior wall shall not terminate adjacent to
the wall or below eaves or parapets, except
as provided in Sections 802.2.5 and 802.3.4.
802.2.5 Direct-Vent Equipment. Listed direct vent
gas utilization equipment shall be
considered properly vented where installed in
accordance with the terms of its listing, the
manufacturers' instructions, and Section 802.8.3.
802.3.4 Mechanical Draft Systems.
802.3.4.1 Mechanical draft systems shall be
listed and shall be installed in accordance
with the terms of their listing and both the
appliance and the mechanical draft system
manufacturers' instructions. [NFPA 54:12.4.3.1]
802.3.4.2 Gas utilization equipment requiring
venting shall be permitted to be vented by
means of mechanical draft systems of either
forced or induced draft design. [NFPA
54:12.4.3.2]
Exception: Incinerators.
802.3.4.3 Forced draft systems and all
portions of induced draft systems under
positive pressure during operation shall be
112
designed and installed so as to prevent
leakage of flue or vent gases into a building.
[NFPA 54:12.4.3.3]
802.3.4.4 Vent connectors serving equipment
vented by natural draft shall not be connected
into any portion of mechanical draft systems
operating under positive pressure. [NFPA
54:12.4.3.4]
802.3.4.5 Where a mechanical draft system
is employed, provision shall be made to
prevent the flow of gas to the main burners
when the draft system is not performing so
as to satisfy the operating requirements of
the equipment for safe performance. [NFPA
54:12.4.3.5]
802.3.4.6 The exit terminals of mechanical
draft systems shall be not less than seven (7)
feet (2.1 m) above grade where located
adjacent to public walkways and shall be
located as specified in Sections 802.8.1 and
802.8.2. [NFPA 54:12.4.3.6]
Department of Redundancy Department