Results 1 to 14 of 14
  1. #1
    Jamie Hawks's Avatar
    Jamie Hawks Guest

    Default TP&R piped into gas line at water heater

    ................................................

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Jamie Hawks; 03-01-2012 at 11:17 PM.
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: TP&R piped into gas line at water heater

    Never seen one in person, but I believe that is the Watts TPR gas valve. There's another name (Watts 210?). It's for a land locked water heater, so that the heater will shut down by stopping the gas flow instead of the relief valve opening and discharging water.

    I'm sure others will have more to say.

    Jim Robinson
    New Mexico, USA

  3. #3
    Jamie Hawks's Avatar
    Jamie Hawks Guest

    Default Re: TP&R piped into gas line at water heater

    That makes sense Jim, it was in a 2nd story condo. Thanks for the reply. I'm going to look up the "watts 210" TP&R valves.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: TP&R piped into gas line at water heater

    Jim nailed it.

    When the T&P relief goes off, the gas shuts down, which immediately stops heating the water, which stops building pressure in the tank, keeping the pressure in the tank to within its safe limits so it does not become a bomb and a rocket and go BOOM! WHOOSH! flying through the air where it lands and takes out something else too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Jamie Hawks's Avatar
    Jamie Hawks Guest

    Default Re: TP&R piped into gas line at water heater

    Thanks guys. I looked it up, your right on!


  6. #6
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: TP&R piped into gas line at water heater

    Just curious, how could it be operated(tested).

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  7. #7
    Tony Watson's Avatar
    Tony Watson Guest

    Default Re: TP&R piped into gas line at water heater

    That is only the temperature side of the T&P valve protection requirement. The heater still needs a pressure relief valve installed. Look at the "three acceptable position sketches" on the web site.
    T.


  8. #8
    Dustin Large's Avatar
    Dustin Large Guest

    Default Re: TP&R piped into gas line at water heater

    Very interesting, learn something new everyday here. Heres a link to some documentation. http://www.plumbersurplus.com/pdf/01146.pdf


  9. #9
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: TP&R piped into gas line at water heater

    Quote Originally Posted by Rick Cantrell View Post
    Just curious, how could it be operated(tested).
    In a search to answer this question I found the following informative link. BTW, it does not mention a testing method.

    i-Course.com : Home Inspector Training Courses Education Online School and Licensing


  10. #10
    Russel Ray's Avatar
    Russel Ray Guest

    Default Re: TP&R piped into gas line at water heater

    Quote Originally Posted by Tony Watson View Post
    That is only the temperature side of the T&P valve protection requirement. The heater still needs a pressure relief valve installed. Look at the "three acceptable position sketches" on the web site.
    T.
    Plumbers here never install the pressure relief valve. I keep copies of the Watts installation instructions in my car, as well as a PDF on the computer, so that I can educate them.


  11. #11

    Default Re: TP&R piped into gas line at water heater

    While the Watts 210 installation instructions say you need a relief valve, it sort of begs the point for the 210 in the first place.
    No where to drain the damn thing! There should be a relief valve on the cold system after the regulator.

    True Professionals, Inc. Property Consultant
    877-466-8504

  12. #12
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: TP&R piped into gas line at water heater

    The instructions illustrate three different methods of installation depending upon how many holes you have to tap in the tank but each includes a TPR somewhere in the piping.

    You would have to heat the water to 210F to test it. Hmmm, maybe that's why its model number is 210? ;-)

    The requirement for these valves would probably be limited to jurisdictions and communities where it is a local ordinance or required by a HOA--not typically found in residential settings.

    Safety controls can be great but the downside is they add one more thing to go wrong or be installed improperly in the first place.

    Bob

    Keep the fire in the fireplace.

  13. #13
    BILL PARR's Avatar
    BILL PARR Guest

    Default Re: TP&R piped into gas line at water heater

    In my early days in the plumbing trade this was common using a Kitson Valve. Same principal as the Watts 210 . I have not seen the valve used (installed) since ASME rated valves hit the market. The old Kitsons were used to control water heater discharge do to temperature overheating. In that time period Watts made pressure relief valves. They also made T&P but the temperature was a meltable plug, when they went off they did not shut. The discharge ran until a valve was manually shut.

    You might be interested in the following.

    On www.parrsplumbing.com click on water heater explosions that will take you to a blog. News paper clippings and photos in the sixties.

    Enjoy the booms ... And read my paper on water heater explosions today!

    Last edited by BILL PARR; 12-26-2009 at 10:00 AM. Reason: spelling & typo

  14. #14
    b reid's Avatar
    b reid Guest

    Default Re: TP&R piped into gas line at water heater

    i don't know if it makes any difference but 210's are not listed for usa just canada. breid............


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •