02-23-2010, 11:30 AM #1
Heater in Crawlspace
Should there be a catch pan under the evaporator coil? I know the drain line should be routed to an approved location, but I'm not sure if a catch pan is required.
Similar Threads:Last edited by brianmiller; 07-02-2013 at 04:16 PM.
-
02-23-2010, 04:08 PM #2
Re: Heater in Crawlspace
never see them around here, may want to check to see if the drain is not blocked , so you know the water is going to an outside location
-
02-23-2010, 05:54 PM #3
Re: Heater in Crawlspace
A secondary drain pan is the least of this installations problems. I would first be concerned with the mold issues that are shown. The condensate is totally wrong, running trap, secondary piped to nowhere, lack of insulation on the suction line. I could smell the mold just looking at the picture, it can't be a healthy home.
-
02-23-2010, 06:07 PM #4
Re: Heater in Crawlspace
thanks,
but is a catch pan required?
and,
um,
I don't see where there is mold.
-
02-23-2010, 06:22 PM #5
Re: Heater in Crawlspace
No, an auxiliary pan under the unit is not required.
You are correct. ALL condensate needs to be routed to outside the crawl space.I know the drain line should be routed to an approved location,
That secondary condensate line is either: a) sucking in all that undesirable crawl space air - YECCH!; or b) blowing out conditioned air - what a waste ... i.e., the secondary condensate line also requires a trap.
-
02-23-2010, 06:57 PM #6
Re: Heater in Crawlspace
thanks...
anyone else see mold in the picture?
-
02-23-2010, 10:17 PM #7