    Default Span Chart

    Does anybody have a span chart for dimensional lumber? I looked at a house today with measured 1.5"x9 inch ceiling joists for the 1st floor. The joists were spaced 16" oc and were spanned 13'. The floor had a lot of squeaking but nothing I would necessarily in and of itself consider a defect.

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Span Chart

    Quote Originally Posted by Nick Ostrowski View Post
    Does anybody have a span chart for dimensional lumber? I looked at a house today with measured 1.5"x9 inch ceiling joists for the 1st floor. The joists were spaced 16" oc and were spanned 13'.

    Sounds like 2x10 (1-1/2" x 9-1/4"), 16" o.c., and is the 13' from edge-of-bearing to edge-of-bearing?

    Finally, and quite importantly, would be the species of wood the joists are.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Span Chart

    Yes Jerry. 13' from edge of bearing to edge of bearing.

    Species of wood? No clue.

    Two thirds of the 1st floor ceiling joists were spaced at 12" oc with similar spans. For some reason, the builders framed the other 1/3 at 16 oc. Maybe they ran out of money.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Span Chart

    From Table R503.3.1(1) Residential sleeping areas
    - Joist Spacing 12" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 13'5" span
    - Joist Spacing 16" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 11'8" span

    - Joist Spacing 12" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 21'0" span
    - Joist Spacing 16" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 19'1" span

    From Table R503.3.1(2) Residential living areas
    - Joist Spacing 12" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 12'3" span
    - Joist Spacing 16" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 10'7" span

    - Joist Spacing 12" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 19'1" span
    - Joist Spacing 16" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 17'4" span

    You can see why species (and grade) are needed to make an informed decision on what might be okay.

    Last edited by Jerry Peck; 02-26-2010 at 08:04 PM. Reason: one line 12" should have been 16", thank you Bruce
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Span Chart

    Quote Originally Posted by Nick Ostrowski View Post
    For some reason, the builders framed the other 1/3 at 16 oc. Maybe they ran out of money.

    Or maybe they planned for something heavy under part of it for the original owners, such as a grand piano or who-knows-what (if anything)??

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Michael Garrity's Avatar
    Michael Garrity Guest

    Default Re: Span Chart

    I have the same figures only at 10psf not 20psf. 2007 NYS R502.3.1

    Let me revise that. NYS code is the same as JP's post.10psf would be the sleeping area and 20psf would be the living area and are under the one table.[residential living areas}

    Last edited by Michael Garrity; 02-25-2010 at 09:27 PM. Reason: late night=sleepy=wrong info

  7. #7
    Join Date
    Apr 2008
    Location
    Massachusetts
    Posts
    195

    Default Re: Span Chart

    A VERY ROUGH rule of thumb is that the allowable span in feet is 1.5 times the depth of the joist in inches: for example, 2x8=12' span, 2x10=15' span, etc. Obviously, the species and grade of lumber, the joist spacing, the loading, the allowed deflection, etc. all need to be known to make a final determination, but the rule-of-thumb is handy to decide if you should look a little closer


  8. #8
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Span Chart

    This topic, as it pertains to home inspections, always catches my interest. Having taken several years of civil engineering, and just building various things, I know my way around span tables very well.

    But..... at what point do we as HIs cross the line and open ourselves up to be accused of undertaking actual "engineering" ?

    I personally won't go very far down this path during the course of a home inspection. Sure, I may come home and look something up on a span table but I'd never, never, never cite my source for saying it's inadequate.

    I seem to remember hearing (probably around here) a story or two of HIs getting their hands slapped for playing engineer.

    To me this is always a funny crossroad between our SOPs and what is reality. Basically, SOPs all say something about just observing and making sure everything looks good. Then, they go on to say the inspection is not technically exhaustive and you aren't required/allowed, etc. to undertake any engineering.

    How can you really do the first without doing the second?


  9. #9
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Span Chart

    Nick

    If you took pictures, it's possible the grade stamp is visible. Check it out.

    Darren www.aboutthehouseinspections.com
    'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)

  10. #10

    Default Re: Span Chart

    To me this is always a funny crossroad between our SOPs and what is reality. Basically, SOPs all say something about just observing and making sure everything looks good. Then, they go on to say the inspection is not technically exhaustive and you aren't required/allowed, etc. to undertake any engineering.
    Hi Matt,

    I guess I've never really worried about it. I don't consider myself doing any engineering work when I cite a code source showing readily available span tables. I'm just citing my source for concern. Of course, I usually start looking at span charts when I see something sagging, feels springy, etc. -- then I can write up the issue, and show the span chart backing up my concern.
    I've had several lawsuit threats from the selling side over the years, but nobody has followed through-- time will tell if I'm going too far I guess.


  11. #11
    Join Date
    Mar 2007
    Location
    Charlotte NC Licensed in NC and SC
    Posts
    597

    Default Re: Span Chart

    Quote Originally Posted by Jerry Peck View Post
    From Table R503.3.1(1) Residential sleeping areas
    - Joist Spacing 12" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 13'5" span
    - Joist Spacing 16" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 11'8" span

    - Joist Spacing 12" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 21'0" span
    - Joist Spacing 16" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 19'1" span

    From Table R503.3.1(2) Residential living areas
    - Joist Spacing 12" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 12'3" span
    - Joist Spacing 12" - 2 x 10 - Spruce-Pine-Fir #3 (worst case/shortest allowed) - 20 psf - 10'7" span

    - Joist Spacing 12" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 19'1" span
    - Joist Spacing 16" - 2 x 10 - Douglas fir-larch SS (best case/longest allowed) - 20 psf - 17'4" span

    You can see why species (and grade) are needed to make an informed decision on what might be okay.

    Jerry, there is a typo for one line in the living area section where you have 12", it should be 16". Was this copied and pasted from the code?

    Bruce King, B.A. King Home Inspections, LLC
    www.BAKingHomeInspections.com
    Certified Master Inspector, Independent Inspectorwww.IndependentInspectors.org

  12. #12
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Span Chart

    I haven't seen 2x10 pass Muni insp or Permit App here over 12'. 2x12 will pass up to about 15,16'. Beyond that it's truss, microlam, etc.
    On older existing house I see it all the time but not on new. On old I don't comment on it, on new I would report it and recommend checking compliance.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  13. #13
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Span Chart

    Citing span tables in the model building code is NOT engineering.
    You can follow the prescriptive or model code or have an engineer design a building.
    Citing a framing member as exceeding the allowable span in the IRC is no different than citing an over fused circuit or a missing GFCI. Not designing, just reporting.
    From Wikipedia

    Engineering is the discipline, art and profession of acquiring and applying technical, scientific, and mathematical knowledge to design and implement materials, structures, machines, devices, systems, and processes that safely realize a desired objective or invention.


    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Span Chart

    Quote Originally Posted by Bruce King View Post
    Jerry, there is a typo for one line in the living area section where you have 12", it should be 16".
    You are correct - I went back and corrected it.

    Was this copied and pasted from the code?
    Unfortunately the table was too complex to copy and paste, so I had to type it out .. and typed it out with a typo.

    The lines were supposed to alternate 12" and 16".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Andrew Christel's Avatar
    Andrew Christel Guest

  16. #16
    Join Date
    Apr 2008
    Location
    Massachusetts
    Posts
    195

    Default Re: Span Chart


  17. #17
    Join Date
    Feb 2009
    Location
    St. Louis, Mo. area.
    Posts
    280

    Default Re: Span Chart

    Quote Originally Posted by Jerry Peck View Post
    ................Unfortunately the table was too complex to copy and paste, so I had to type it out .. and typed it out with a typo. ................
    You mite have the same probrem I habe. My keybord can't spel wurth a darn ether! I neeed to replac it!

    Last edited by Michael Chambers; 03-02-2010 at 11:23 PM. Reason: To correc the speling!

  18. #18
    rog_arch's Avatar
    rog_arch Guest

    Default Re: Span Chart

    When there is no stamp visible what Fb should be assumed?