Multiple grounds under one terminal
Was this ever allowed? (Maybe a poor choice of words. It was obviously "allowed" 19 years ago by the AHJ.
Similar Threads:
-
03-27-2010, 12:49 PM #2
Re: Multiple grounds under one terminal
no, if you look at the label on the panel it will tell the number and size of the conductors allowed in that lug and the other ground bars in the panel. Make sure you look at it correctly most allow only one grounded conductor but do allow multiple grounding conductors.
-
03-27-2010, 01:30 PM #3
Re: Multiple grounds under one terminal
Forgot I took a pic of the label.
-
03-27-2010, 01:59 PM #4
Re: Multiple grounds under one terminal
That label shows that 1 #6 up to 1 2/0 are allowed no multiple conductors and no conductors smaller thal #6.
-
03-28-2010, 08:15 AM #5
Re: Multiple grounds under one terminal
Common practice years ago to twist all branch circuit grounds and go for one termination.
The SEP installed when my house was built in 1982 was done that way. I had the SEP replaced last fall and the electrician corrected all the 'old ways' and did it right (at least to current standards).
-
03-28-2010, 01:06 PM #6