Results 1 to 12 of 12
Thread: Panel on ceiling
03-25-2010, 06:44 PM #1
Panel on ceiling
Anyone know the NEC # for a panel located on ceiling. Thanks.
03-25-2010, 06:51 PM #2
Re: Panel on ceiling
Not allowed like that.
They were only tested and listed to be installed vertically on a vertical surface (such as a wall, support stand, etc.). That is how they were tested for heat rise, ability to dissipate heat, breakers staying in place, and all the other factors which could affect a panel installed horizontally face down like that, not to mention what could unexpectedly fall out into your face and be energized, resulting a not real pretty sight.
I've seen a few installed like that and have written them all up for correction.
03-26-2010, 09:27 AM #3
NEC 240.24(A) also requires the circuit breaker [center of the grip] be not more than 6'7" above the floor.
03-26-2010, 04:05 PM #4
03-26-2010, 06:04 PM #5
Lets try this one on for size:
Nec article 240.33
Enclosures for overcurrent devices shall be mounted in a vertical position unless that is shown to be impracticable. Circuit breaker enclosures shall be permitted to be installed horizontally where the circuit breaker is installed in accordance with 240.81. Listed busway plug-in units shall be permitted to be mounted in orientations corresponding to the busway mounting position
03-27-2010, 01:38 PM #6
Sometimes appearances alone are not enough to explain things.
I suspect that is not a 'panel' as much as a 'disconnecting means.' As such, there's no code, or even 'trade practice,' issue, assuming that the placement of the disconnect makes sense as compared to the location of whatever is being disconnected. That is, what might appear to be a bad placement might make perfect sense once you place yourself in a position to service the equipment.
In that regard, context is everything. For example, a disconnect for the HVAC equipment located above a suspended ceiling might also be above the ceiling, near the equipment. The "handle height rule" would not be applied in that circumstance.
03-27-2010, 05:27 PM #7
03-27-2010, 06:06 PM #8
03-28-2010, 09:02 AM #9
It is just as Jerry described, a panel with 4 breakers.
03-28-2010, 09:06 AM #10
Picture.
03-28-2010, 10:13 AM #11
?? John - I don't know where you get your 'trade practices' information, but all the previous code sections mentioned in Art. 240 are overcurrent protection [as in breakers] rules, not panel rules.
BTW - you are correct, there is no code prohibiting a panel from being installed horizontal, upside-down, etc., but if you choose to install breakers in that panel then Art. 240 prohibits such for the breakers.
03-28-2010, 01:19 PM #12