Results 1 to 7 of 7

Thread: Electric Heater

  1. #1
    MichelleCoupe's Avatar
    MichelleCoupe Guest

    Default Electric Heater

    Hi,
    I just had a quick question. Is it illegal to have an electric water heater in the bedroom closet?? Thanks in advance.

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Electric Heater

    It is allowed to have an electric WH in a bedroom closet, as long as it is accessible for servicing.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    mike huntzinger's Avatar
    mike huntzinger Guest

    Default Re: Electric Heater

    I would make shure a catch pan is in the closet too


  4. #4
    Teresa Testarosa's Avatar
    Teresa Testarosa Guest

    Default Re: Electric Heater

    Quote Originally Posted by Rick Cantrell View Post
    It is allowed to have an electric WH in a bedroom closet, as long as it is accessible for servicing.
    Yeah, I agree.. It is okey, long as it is accessible...


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Electric Heater

    Quote Originally Posted by Teresa Testarosa View Post
    Yeah, I agree.. It is okey, long as it is accessible...

    ... define "accessible".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Electric Heater

    Jerry's comment got me to look up the requirements.
    My original post is incomplete.
    ("It is allowed to have an electric WH in a bedroom closet, as long as it is accessible for servicing.")
    An electric WH can be located in a bedroom closet if/when other conditions are met.
    It is not likely that all the conditions are being met.
    Specifically the requirement that the space not be used for " Storage" and the requirement for " clearance to combustibles".
    Below are some of the requirements that I found that apply.
    There are other requirements that apply that I did not show.

    CHAPTER 28
    WATER HEATERS
    P2801.2 Installation.Water heaters shall be installed in accordance
    with this chapter and Chapters 20 and 24.
    P2801.3 Location. Water heaters and storage tanks shall be
    located and connected to provide access for observation, maintenance,
    servicing and replacement.
    P2801.4 Prohibited locations. Water heaters shall be located
    in accordance with Chapter 20.

    CHAPTER 20
    BOILERS AND WATER HEATERS


    M2005.3 Electric water heaters. Electric water heaters shall
    also be installed in accordance with the applicable provisions
    of Chapters 33 through 42.

    CHAPTER 24

    FUEL GAS
    (Chapter 24 does not apply)

    SECTION E3305
    EQUIPMENT LOCATION AND CLEARANCES
    E3305.1 Working space and clearances. Sufficient access
    And working space shall be provided and maintained around all
    electrical equipment to permit ready and safe operation and
    maintenance of such equipment in accordance with this section
    and Figure E3305.1.
    E3305.4 Location of working spaces and equipment.
    Required working space shall not be designated for storage.

    E4001.2 Installation. Appliances and equipment shall be
    installed in accordance with the manufacturer’s installation
    instructions. Electrically heated appliances and equipment
    shall be installed with the required clearances to combustible
    materials.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Electric Heater

    .

    .



    .

    .

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •