Thread: No main handle
04-29-2010, 05:01 AM #1
No main handle
Pending sale on this house was thwarted by the discovery of service equipment with main lugs only. Someone inserted old 60 amp entrance cable into a new 150 amp main lug panel. My question is does the entire panel have to be changed out, or is it ok to back feed a 60 amp breaker with the SEU? Thanks for prompt, thoughtful replies only.
04-29-2010, 05:28 AM #2
Re: No main handle
If you can get a listed hold-down bracket and it can be used in that panel, you could install the 60 and backfeed the panel. Some hold-downs are not for use with all panels. Square D has one that is only for the smaller panels.
04-29-2010, 06:46 AM #3
Re: No main handle
04-29-2010, 07:11 AM #4
Re: No main handle
Thank you gentlemen for prompt, courteous replies. Further investigation reveals that this Square D panel allows for conversion to a main breaker by simply removing the lugs and bolting to the bus bars. This still leaves the problem of the 60 amp entrance cable as you pointed out, Scott. I am recommending a wire upgrade be performed at the same time.
04-29-2010, 05:10 PM #5