Good Morning,
I inspected a house a couple days ago and found a sub panel in the laundry room. The panel was not accessible to the home owner because rivets were put in the panel. The pan does not breakers and just seems like a junction box. The main panel is directly above it on the second floor. If access is denied to the occupant does this need to have breakers?
Barrington Sheffield
Aggie Property Inspections, LLC
Duluth, GA
http://www.myapinspections.com
Similar Threads:
-
05-03-2010, 07:33 AM #2
Re: Can a electrical subpanel act as a junction box?
Sounds like this was the orginal location for the panel. A new panel was installed in a different location (upstairs).
This is not uncommon and is allowed.
Someone else on the board can tell you more.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
05-03-2010, 06:18 PM #3
Re: Can a electrical subpanel act as a junction box?
This is allowed and is quite common in my area. Many times older panels get gutted and are used as junction boxes. They pull the feeds to the new panel location.
-
05-03-2010, 07:08 PM #4
Re: Can a electrical subpanel act as a junction box?
Except that one was not gutted, they left the interior in there.
If they remove the interior it would probably be fine, but not with the interior still in there. (Removing the interior "panelboard" from the "cabinet" leaves you with just a "cabinet", and that use would be okay.)
-
05-05-2010, 05:33 AM #5
Re: Can a electrical subpanel act as a junction box?
Jerry P,
Why is the presence of the interior components harmful?
Darrel Hood
DILIGENT PROPERTY SERVICES
-
05-05-2010, 02:15 PM #6
Re: Can a electrical subpanel act as a junction box?
The remaining interior components (bus bar) was probably difficult to remove so they just left it there. It most likely has no way of becoming energized and is not a concern. However most times you see the panel entirely gutted.
-
05-05-2010, 03:26 PM #7
-
05-05-2010, 06:22 PM #8
Re: Can a electrical panel act as a junction box?
Because:
- With the panelboard interior left in place it is "still" a panelboard which is not allowed to be used as a junction box.
- The panelboard interior bus bars, terminal bars, etc., have sharp edges which could damage the insulation of the wiring laying on them.
- With the panelboard interior left in place there is the risk that a damaged conductor could energize the panelboard, which could then lead to other conductors becoming energized.
- Because the listing on the panelboard in that enclosure would not allow it to be used that way - the only way is to use the cabinet *only* and then follow the listings for the cabinet and the requirements in the code for cabinets.
- Someone could intentionally energize the bus bar and insert some breakers, making that into one large dangerous mess.
- The above should do for starters.
-
05-05-2010, 07:11 PM #9
Re: Can a electrical subpanel act as a junction box?
Is it OK to use rivets on a "junction box"?The panel was not accessible to the home owner because rivets were put in the panel.
-
05-06-2010, 04:54 PM #10
Re: Can a electrical panel act as a junction box?
-
05-06-2010, 05:05 PM #11
Re: Can a electrical subpanel act as a junction box?
Just an observation....if there is not a main breaker before the SEC/feeders get to this panel you could have both fused and unfused wires in this panel and that is a no-no. Most likely not an issue but worth mentioning.
-
05-06-2010, 05:17 PM #12
Re: Can a electrical subpanel act as a junction box?
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
05-06-2010, 05:59 PM #13
Re: Can a electrical panel act as a junction box?
James,
Good point.
I presumed the 4-wire feeders were ... well, "feeders" ... as they are 4-wire. Typically (but not always) service entrance conductors will be 3-wire instead of 4-wire.
Service entrance conductors, being unfused at their source, are not allowed to run with other conductors while feeder conductors, being protected at their source, are allowed to be run with other conductors.
-
05-07-2010, 05:51 AM #14
Re: Can a electrical subpanel act as a junction box?
Jerry & Nick,
Thanks for your replies to my question. They make sense.
Darrel Hood
DILIGENT PROPERTY SERVICES
-
05-07-2010, 06:58 AM #15
Re: Can a electrical subpanel act as a junction box?
From what I understand , it is allowed as long as the "guts" have been removed, it's accessible, then it pretty much, basically becomes a giant junction box.
-
05-07-2010, 11:22 AM #16
Re: Can a electrical panel act as a junction box?
It looks to me like the rivets are in the hinged door, but the cover was removable by the screws. That's OK, right? With the breakers gone, it would Not be OK if the hinged door was Not riveted, IMO.
I believe the point was that the bus bars should have been removed, and that those large cables may not be service conductors. There are enough questions there to call for repair.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
05-07-2010, 03:54 PM #17
Re: Can a electrical panel act as a junction box?
-
05-07-2010, 06:34 PM #18
-
05-15-2010, 12:22 AM #19
Re: Can a electrical subpanel act as a junction box?
Hi all. Long-time lurker and Inspector - first post.
I don't think I would have 'popped' any rivets to take a look inside the box. Not without the homeowner's permission anyway. Even then I would be very hesitant. Undoing a few screws is a different matter. If I considered the panel/box to be suspicious, I would have called it just that and encouraged further evaluation by a licensed qualified professional. Is that too 'passing-the-buckish'?