    Default Is a bare neutral ok here?

    Service panel, 1989 home. Looks like metal conduit from meter can on the left. At the weatherhead, the neutral was insulated, so there's a splice at the meter?

    Is a bare neutral ok here?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Is a bare neutral ok here?

    Quote Originally Posted by John Kogel View Post
    At the weatherhead, the neutral was insulated, so there's a splice at the meter?
    The neutral coming out the top of the weatherhead is typically insulated, it ties to the neutral/ground from the overhead service drop conductors, it then lands on the neutral/ground connection at the meter, grounding the meter can.

    From there, the neutral/ground can run to the service equipment as either bare or insulated, so ...
    Is a bare neutral ok here?
    Given the above scenario, yes, the neutral/ground is allowed to be bare to the service equipment.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Is a bare neutral ok here?

    Thanks, Jerry. I have another question coming shortly.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Is a bare neutral ok here?

    Regarding the bare/insulated splice: service conductors can be spliced w/certain conditions but not within a raceway w/o an accessible cover.

    Funny how code allows the grounded/neutral conductor to be run thru a metallic raceway without bonding both ends, yet the GEC cannot.
    Under a major fault, that grounded conductor would carry many more amps than say, a GEC to a few earthing rods. Just a rambling thought.
    Bob Smit, County EI