i inspected a condo today and found this in the service panel. It doesn't look correct, i don't think the terminal/lug is listed for multi / tapps.Not sure and would like input from some of the more experinced HI's. There is no ground bus bar.
Similar Threads:
-
07-19-2010, 04:59 PM #2
Re: This doesn't look correct
"Mike"
Of course its not right.
Even when a terminal is allowed to have multiple conductors, they have to be of the same size and type.
You have a large stranded ground and solid wires of differing sizes.
Never would you find a panel with terminals rated for that many, let alone different types and size conductors in the same terminal.
It is an unsatisfactory condition and is deficient.
-
07-19-2010, 05:02 PM #3
Re: This doesn't look correct
The lug should be stamped with the number and size of conductors allowed that lug I would guess from installing many simular lugs only allows one conductor from a #6 to 1/0.
-
07-19-2010, 05:08 PM #4
-
07-19-2010, 05:12 PM #5
Re: This doesn't look correct
Thanks guy's. Love this site.
-
07-25-2010, 06:22 PM #6
Re: This doesn't look correct
-
07-25-2010, 07:34 PM #7
Re: This doesn't look correct
The only time I call out a grounding lug that has been added is if it has been mounted with sheet metal screws. If it is bolted to the panel or installed into a tapped hole it is installed properly IMHO. That is why lugs are made and sold...to be installed where they are needed.
-
07-26-2010, 10:18 AM #8
Re: This doesn't look correct
I will agree that there should be a ground bus, and this lug should not be used this way. Is this a subpanel?
Randall Aldering GHI BAOM MSM
Housesmithe Inspection
www.housesmithe.com
-
07-26-2010, 02:11 PM #9
Re: This doesn't look correct
Randy,
Yes it's a "sub panel" The main service panel was a nightmare. enclosed in an exterior utility closet, Appox 10' off the ground and i couldn't get in to look at it & 1970's FPE panel. You can imagine the shape it was in, this unit is next to the Gulf of Mexico.
-
07-26-2010, 05:46 PM #10
Re: This doesn't look correct
-
07-27-2010, 04:50 AM #11
Re: This doesn't look correct
Bill, It was written up. As you can see in the pic. there wasn't room for me to get my head in the closet ( the main panel is above the meter all the way to the left). I don't understand why they let them do it like this around here but I see it more often than not.