Results 1 to 12 of 12
Thread: Refrigerant leakage from coil
08-22-2010, 06:41 AM #1
Any thoughts on whether this is refrigerant leaking from the coil.
08-22-2010, 06:49 AM #2
Re: Refrigerant leakage from coil
08-22-2010, 09:37 AM #3
Doesn't look to be a typical refrigerant leak, looks like something nasty dripped onto the equipment though.
08-22-2010, 03:22 PM #4
I would check for a cracked heat exchanger if that coil is on top of a furnace. Can't tell from the pic whether ductwork goes through the floor. If so it could be leakage from above. Wouldn't hurt to remove the screws from the front of the coil and just visually check the txv if so equipped.
08-22-2010, 06:42 PM #5
who spilled my soda?
Looks like it dripped from above the coil.
You usually see filter driers outside at the condenser so I'm wondering what went on that this was added inside. Maybe a changeout reusing the old lineset and may or maynot have flushed it.
I'd look closely at the filter rack to see how well it seals and how much crap has blown past it. Is the blower all crudded up with dust bunnies in the plenum? Did someone throw Coca Cola into the fan?
Check the condensate drain to see if this stuff is internal or external.
08-22-2010, 09:47 PM #6
Is it an oil furnace?
08-23-2010, 07:37 AM #7
08-23-2010, 05:04 PM #8
My guess is that they used a condensate tape like Prestite (the gooey stuff) to seal the duct joint. While made for cold surfaces such as condensate and suction lines, it tends to "melt" and bleed under heat and thus use in this manner may be what happened when the furnace was running.
Definitely not a refrigerant leak.
08-23-2010, 06:57 PM #9
08-24-2010, 06:03 PM #10
Possible condensate drain is stopped or not draining as fast as should and overflowing which happens in my area a lot. Most are not caught right away. many that are in a basement or crawl space around here will go unnoticed for a while (unless an inspection or failure happens). There are many in attics here which then the secondary drain pan under the entire system clogs and overflows then part of the ceiling comes down. A lot of algae and mold issues here anywhere a little moisture is and usually will clog a 3/4 inch drain commonly used here.
08-24-2010, 06:15 PM #11
I have been on numerous unidentifiable leak calls in my 25 years of service work. While I agree that a refrigerant leak is not probable, it is still possible. The oil will contaminate with the surrounding dirt, dust, or anything else on the coil and look bad. My original thought and what I still believe is a cracked heat exchanger. Only an in depth test of the system will reveal the true reason for this. Condensate problems do not leave those type of stains.
08-24-2010, 06:25 PM #12