Results 1 to 7 of 7
Thread: Slope of furnace vent
-
09-23-2010, 08:07 AM #1
Slope of furnace vent
Garage furnace with an induced draft vent. It is allowed to slope downward? Could not find any installation instructions. Place was built in 07
Similar Threads:
-
09-23-2010, 08:29 AM #2
Re: Slope of furnace vent
I don't see those types of units around here.
Is that a condensate stain on the plate beneath the flue pipe?
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
09-23-2010, 08:34 AM #3
Re: Slope of furnace vent
No way.
The Simpson Dura-Vent instructions I have say that any "horizontal" sections must slope upwards away from the appliance at least 1/4" per foot. I don't think it would say that if you were allowed to vent vertical sections down as shown.
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
09-23-2010, 08:46 AM #4
Re: Slope of furnace vent
Induced draft is still considered natural draft and must be installed as such. As John said, needs correct slope.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-24-2010, 07:03 AM #5
Re: Slope of furnace vent
Agreed as flat out wrong.

-
09-24-2010, 07:09 AM #6
Re: Slope of furnace vent
Also, clearance from venting to gas pipe not good, no sediment trap on gas line, clearance of unit to ceiling could be suspect.
-