Results 1 to 13 of 13
Thread: Home Inspector
11-02-2010, 10:35 AM #1
Home Inspector
Per NEC are AFCI's now required on dedicated circuits such as ones to refeigerator, washing machine and such?
11-02-2010, 10:51 AM #2
Re: Home Inspector
The AFCI requirement is based on the circuits location, not its usage. You might want to read Article 210.12(B).
11-03-2010, 04:24 PM #3
Re: Home Inspector
Like Jim Port stated, Arc-Fault protection is required for areas /rooms that the circuit supplies, not the load of the circuit.
Arc-Fault Circuit Interrupter Protection is required for all 120 volt ,15 & 20 amp, single phase circuits supplying outlets installed in Family rooms,dining rooms, living rooms, parlors, libraries,dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas.
Kitchens, bathrooms, laundry rooms, basements, garages, do not need Arc-Fault protection
11-04-2010, 10:07 AM #4
Re: Home Inspector
Ken,
You might add that AFCI not required for dedicated circuit to appliance, if you have a ceiling fan in bedroom an AFCI will probably trip due to motor. The work around to the problem of new requirement, as I have understood.
Though it would require a specific direction in wiring diagram and the electrician to take notice of it when they pull the wiring. Most are still running a ceiling box the way they use to for a light fixture. Unless it is caught early and corrected the home owner is up the creak when they want to put in a ceiling fan with a AFCI on that line.
11-04-2010, 04:13 PM #5
Re: Home Inspector
Ceiling Fans cause problems with AFCI's - Buy a new Fan
-If your putting a ceiling fan in one of those areas / rooms listed in the NEC, ceiling fans must be on the AFCI circuit. There is no way to run the circuit to get around the afci protection requirement, for ceiling fans.
As far as dedicated circuits for appliances not requiring AFCI prtotection, It will depend on the location of said appliance.
Put a microwave circuit at the bar in the family room - Guess what? AFCI required.
An air conditioner is considered to be an appliance according to the definition of appliance in the NEC. Install a dedicated 120 volt line for a window air conditioner - AFCI required.
So Like it was stated prior:
The requirement for AFCI protection is based on the location of the circuit - NOT the load / usage of the circuit.
11-04-2010, 04:49 PM #6
Re: Home Inspector
The above needed repeating.
AFCI protection is LOCATION dependent, not what is on the circuit.
It's all about "location, location, location", and nothing to do with what is connected in that location.As far as dedicated circuits for appliances not requiring AFCI prtotection, It will depend on the location of said appliance.
11-05-2010, 07:51 AM #7
Re: Home Inspector
Although Virginia hasn't officially adopted the 2009 IRC yet, it should be in effect for new construction permitted in or after April 2011. I got the scoop from a code council person that Virginia had waved the new AFCI provisions leaving the only the original bedroom protection.
OFF TOPIC:
FLASH, Fresh from the rumor mill --- Beware the 2012 IBC/IRC. Just prior to the October special council session in Charlotte NC, the section on energy provisions was reported to be as thick or thicker than the rest of the code sections combined. From what I have heard, Energy Audits may become mandatory on new construction. It's a matter of the DOE pressuring the states to do something about energy conservation themselves or live with what the DOE requires. You might want to seriously consider what it would take for training, equipment, and certification. Hopefully, I'll be retired by that time (HA!).
Stu, Fredericksburg VA
11-05-2010, 08:43 AM #8
Re: Home Inspector
Ben J.
Thanks.
After posting I thought over my conversation with Master Elect.
Did have things mixed up as to location and use criteria.
The conversation was on quite a few items. Ceiling fans and AFCI only being part of discussion.
02-10-2011, 07:44 AM #9
Re: Home Inspector
www.inspectaz.com
02-10-2011, 07:46 AM #10
Re: Home Inspector
Hate to bust your bubble and allow your ego to drip all over, but ...
If your skills at electrical work are twice as good as your skills with the language - I would NOT want you to even change a light bulb.
Your post makes me think that you think that 'only you' are qualified to do home inspections relating to electrical, yet your work is likely some of the very work home inspectors in your area have to write up as poor work and in need of correction.
Clean up on aisle 3, fluid and ego all over the floor!
02-10-2011, 03:29 PM #11
Re: Home Inspector
That looks like it came from bad translation software.
12-26-2021, 10:14 AM #12
Re: Home Inspector
Where is the original post? Not sure I see what all the replies are in response to, but would otherwise like to help.
- electrician in st catharines
12-31-2021, 04:10 PM #13
Re: Home Inspector
He was asking whether equipment on dedicated circuits was exempt from the AFCI requirement. I guess he wasn't aware that conceptually the AFCI requirement is based on the risk to occupants in the event of an electric fire starting in the areas covered by 210.12. the problem with this is naturally that 210.12 only lists the areas the outlets are located, and can't really include the areas that the wiring passes through en route.
