Results 1 to 14 of 14
  1. #1
    Ron Bishop's Avatar
    Ron Bishop Guest

    Default Overheatd AC disconnect

    Attached is a pic of an overheated AC disconnect. What would cause that? Should a breaker have tripped before this overheating occured? Can an AC unit be run if the air handler is off at the breaker?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Overheatd AC disconnect

    My guess as to the cause would be a short circuit, which allowed a lot of current to flow through the switch. Perhaps the disconnect switch itself developed a partial short, where the contacts were just barely touching.

    Assuming there is a breaker correctly installed in a panel ahead of this disconnect, the breaker would not trip until the current exceeded its rating of say 30 - 40 amps. It doesn't take much heat to melt plastic.
    Just a guess, given the one pic and no other info.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Overheated AC disconnect

    A bad connection at either a terminal or the the pull-out could cause overheating like that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Overheatd AC disconnect

    240 volts x 50 amps = 12,000 watts with a properly operating 50 fuse or breaker. Imagine 10 space heaters or blow dryers worth of heat concentrated on that plastic. One loose wire inside that disconnect on a properly operating a/c could easily account for that destroyed disconnect.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  5. #5
    Bob Winchester's Avatar
    Bob Winchester Guest

    Default Re: Overheatd AC disconnect

    This is caused by a loose connection, the terminals not tightened on the wires that are installed. I use a disconnect like that all the time. It is non fused and a simple pull out. There is a solid copper connection between the line and load terminals on each line of the 240 volts. This is rated at 60 amps and it is probably a 30 amp or less condenser unit. Loose wires get very very hot. I've seen them do worse damage than this. This disconnect must now be replaced. Properly connected wires will let a disconnect such as this operate for many years.


  6. #6
    Join Date
    Jan 2008
    Location
    Orlando, FL
    Posts
    54

    Default Re: Overheatd AC disconnect

    Quote Originally Posted by Bob Winchester View Post
    This is caused by a loose connection, the terminals not tightened on the wires that are installed. I use a disconnect like that all the time. It is non fused and a simple pull out. There is a solid copper connection between the line and load terminals on each line of the 240 volts. This is rated at 60 amps and it is probably a 30 amp or less condenser unit. Loose wires get very very hot. I've seen them do worse damage than this. This disconnect must now be replaced. Properly connected wires will let a disconnect such as this operate for many years.
    I agree with Bob. I had a new geothermal system installed a couple of months ago and about an hour after the system was started, I was connecting the HRU and started smelling something hot. I looked around and finally noticed the disconnect was very hot. When the installed the new system, they never checked to make sure the old connections were tight. I don't know what would have happened if I had not been nearby.

    Robert Sole
    REM Inspections LLC
    www.REMinspections.com, Orlando, Oviedo

  7. #7

    Default Re: Overheatd AC disconnect

    Quote Originally Posted by Ron Bishop View Post
    Attached is a pic of an overheated AC disconnect. What would cause that? Should a breaker have tripped before this overheating occured? Can an AC unit be run if the air handler is off at the breaker?
    Loose connection.


  8. #8
    Bob Winchester's Avatar
    Bob Winchester Guest

    Default Re: Overheatd AC disconnect

    I just replaced a 50 amp GFCI breaker today because one of the terminals was burned off the disconnect and it was tripped of course. The terminals were loose. I'm surprised the other terminal didn't go up in smoke too. I had to strip back the wire about 6" to get to good wire. It's much cheaper to tighten the terminals than to replace $90 breakers. Heat is an enemy of electrical wiring. Make sure everything is tight. If a terminal is discolored it is probably loose as long as the wire size is correct.


  9. #9
    Join Date
    Jul 2010
    Location
    Tennessee
    Posts
    66

    Default Re: Overheatd AC disconnect

    Could also be simply a loose or poor connection. The melt down looks like heat over a long period of time -- something a bad connection would produce.


  10. #10
    Bob Winchester's Avatar
    Bob Winchester Guest

    Default Re: Overheatd AC disconnect

    Why does everybody keep posting that it "might" be a loose connection like it was their idea? That is what the cause was. Case closed.


  11. #11
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Overheatd AC disconnect

    Bob W., The case isn't closed.....without the dead front removed, we can only guess. Nobody mentioned a ground fault as of yet, neither has the idea of the disconnect being mis-wired from the start been mentioned. Since this is an outdoor installation, a mass overcurrent such as lightning could have found its way to this unit by various paths.

    I have also witnessed all kinds of destruction both as an E-contractor and as an Inspector. One size does not fit all in the destruction zone.
    We need a look under the sheets.


  12. #12
    Bob Winchester's Avatar
    Bob Winchester Guest

    Default Re: Overheatd AC disconnect

    That picture is long term heat, not instantaneous heat. The breaker didn't blow so faulting to ground is not the obvious. The terminals on the left side of the disconnect were loose. It's probably still working too. That is what is sad.


  13. #13
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Overheatd AC disconnect

    Ron Bishop, can U get more pics of the disconnect with dead front removed? The assumers' are restless.


  14. #14
    ray jackson's Avatar
    ray jackson Guest

    Default Re: Overheatd AC disconnect

    As an A/C technician I see this all the time. That is a cheap disconnect. Usually the wires aren't tight. They could also be aluminum wire without an anti-oxide compound. Or it could be the "knife blade" connector not making good contact.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •