    Looked in a ITE panel today and found a double tap @ the main lug, but other end went to a ITE Safety Switch box. Would this be acceptable

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double Tap At Main Lug

    No, that lug is good for only one conductor.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Double Tap At Main Lug

    Don't forget all those neutrals and grounds in the same terminals with each - that is not allowed either.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Roger Frazee's Avatar
    Roger Frazee Guest

    Default Re: Double Tap At Main Lug

    To add

    Appears there is no identified neutral ( not a big deal but just pointing it out)

    You probably mentioned it in your report but they could use a few lessons on properly fastening those nm cables in the photo of the safety switch.


  5. #5
    LEO304E CARR's Avatar
    LEO304E CARR Guest

    Default Re: Double Tap At Main Lug

    Quote Originally Posted by Roger Frazee View Post
    To add

    Appears there is no identified neutral ( not a big deal but just pointing it out)

    You probably mentioned it in your report but they could use a few lessons on properly fastening those nm cables in the photo of the safety switch.

    All conductors shuld have a seperate connection


  6. #6
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: Double Tap At Main Lug

    Quote Originally Posted by LEO304E CARR View Post
    All conductors shuld have a seperate connection
    Often it's ok to have more than one equipment grounding conductor at the same terminal.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)