Vent through attic
Odd installation. This image is taken from the attic, first floor. The vent is about 10" from the top of the box where it enteres the roof deck, where a firestop is installed. IMO, this should be an enclosed chase or a firestop should be in place at this ceiling height.
What say you?
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
11-23-2010, 08:08 PM #2
Re: Vent through attic
-
11-23-2010, 08:57 PM #3
Re: Vent through attic
R1003.19 Chimney fireblocking
All spaces between chimneys and floors and ceilings through which chimneys pass shall be fireblocked with noncombustible material securely fastened in place.
I was suggesting the chase because it's blocked at the roof which is approx 10' from the top of the box. If the vent was fireblocked I.E. chase, the metal stop at the roof would meet the minimum standard. Yes?
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
11-24-2010, 09:46 AM #4
Re: Vent through attic
Are you designing a repair or calling out a defect?
-
11-24-2010, 02:46 PM #5
Re: Vent through attic
R1003 is for masonry chimneys. This is a factory built chimney. R602.8 and thus R302.11 are your reference under the 2009 IRC. Before this, wasn't Calif under the UMC, which called for vertical fireblocking?
Keep the fire in the fireplace.
-
11-25-2010, 07:54 AM #6
Re: Vent through attic
That's the case in my Jurisdiction, until next month then they go IRC.