    Default Two flues, one fireplace

    This chimney has two flues, pretty normal. But what's odd is, they are both open to a normal sized wood-burning fireplace. Has anyone seen this? How would draft be affected? There would be a weaker draft, but twice the capacity for smoke.

    The damper was stuck open. Big drafty hole in the wall, and it is pulling away from the house, too.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Two flues, one fireplace

    Flue size is dependent on the opening at the front of the firebox. The mason may have not been able to get a single flue tile that was large enough.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Two flues, one fireplace

    Quote Originally Posted by Gunnar Alquist View Post
    Flue size is dependent on the opening at the front of the firebox. The mason may have not been able to get a single flue tile that was large enough.
    Well that is the surprising part. The fireplace opening is no larger then any normal fireplace. You can see that it has a standard screen in front of it. The flue tiles are large enough that one flue would have been ample, IMO.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Two flues, one fireplace

    It looks like it does have a drafting issue. Just looking at the smoke stained rockwork on the front of the fireplace I would say that it is backdrafting pretty good. Without seeing the throat and smoke shelf area it is difficult to tell by the photos. I would just report it as unconventional and tell my client that unconventional items perform in unconventional ways! Without seeing a real fire in that fireplace and how it performs everything is going to be a guess.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  5. #5
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Two flues, one fireplace

    I owned a house with exact fireplace. Stone face and two flues. On real cold days I would have to light several sheets of loose news paper just to get the draft started.

    The beatings will continue until morale has improved. mgt.

  6. #6
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Two flues, one fireplace

    Quote Originally Posted by Vern Heiler View Post
    I owned a house with exact fireplace. Stone face and two flues. On real cold days I would have to light several sheets of loose news paper just to get the draft started.
    Thanks Vern. Poor draft was my guess.
    Was there any advantage to the double flue? Like Scott says, it goes against convention.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  7. #7
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Two flues, one fireplace

    Quote Originally Posted by John Kogel View Post
    Thanks Vern. Poor draft was my guess.
    Was there any advantage to the double flue? Like Scott says, it goes against convention.
    None that I could tell. On windy nights sometimes it would blow a puff into the house. I was going to block off one but sold the house before I got around to it.

    The beatings will continue until morale has improved. mgt.

  8. #8
    Ashley Eldridge's Avatar
    Ashley Eldridge Guest

    Default Re: Two flues, one fireplace

    Quote Originally Posted by John Kogel View Post
    This chimney has two flues, pretty normal. But what's odd is, they are both open to a normal sized wood-burning fireplace. Has anyone seen this? How would draft be affected? There would be a weaker draft, but twice the capacity for smoke.

    The damper was stuck open. Big drafty hole in the wall, and it is pulling away from the house, too.
    Actually John, that is considered acceptable and recognized by most building authorities as a means of providing sufficient area to the flue (normally for larger fireplaces). The tiles should be in contact with each other at the bottom and supported by masonry on the remaining 3 sides.

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  9. #9
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Two flues, one fireplace

    Quote Originally Posted by Ashley Eldridge View Post
    Actually John, that is considered acceptable and recognized by most building authorities as a means of providing sufficient area to the flue (normally for larger fireplaces). The tiles should be in contact with each other at the bottom and supported by masonry on the remaining 3 sides.

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America
    Though it might be recognized as acceptable, mine sucked! Well, "didn't suck"!

    Do you have a chart of the dimensions for flue size to fireplace size?

    The beatings will continue until morale has improved. mgt.

  10. #10
    Evan Wray's Avatar
    Evan Wray Guest

    Default Re: Two flues, one fireplace

    The mason must have liked lots of draft on his fireplaces, he may have had a problem with draw in a heavily treed area previously. The real issues are the home owners heating dollars going up the chimney and the settling away from the house which may have stopped. Anyway just wanted to say hi to John K. I used to be a southern Van. Islander also. Merry green Christmas from the city of snow and ice.


    Evan W. mason ,Internachi member.


  11. #11
    Ashley Eldridge's Avatar
    Ashley Eldridge Guest

    Default Re: Two flues, one fireplace

    Quote Originally Posted by John Kogel View Post
    This chimney has two flues, pretty normal. But what's odd is, they are both open to a normal sized wood-burning fireplace. Has anyone seen this? How would draft be affected? There would be a weaker draft, but twice the capacity for smoke.

    The damper was stuck open. Big drafty hole in the wall, and it is pulling away from the house, too.
    Quote Originally Posted by Vern Heiler View Post
    Though it might be recognized as acceptable, mine sucked! Well, "didn't suck"!

    Do you have a chart of the dimensions for flue size to fireplace size?

    Vern, the acceptable rule is that for square liners or those with less than a 2-to-1 ratio (meaning the width of the tile is no more than twice the depth) the flue should be 1/10th the area of the fireplace opening. If the flue has a greater ratio it should be 1/8th the area of the fireplace. For round flues the flue should be 1/12th the area of the fireplace opening.

    One exception to that rule is the Rumford design. If the design features of that fireplace are followed the flue can be up to 1/20th the area of the fireplace opening. The simple formula for the Rumford is;
    if x designates the depth, then the width is 2x and the height is 3x.

    While the IRC specifies a minimum depth of a conventional firebox to be 20 inches, the Rumford can be as shallow as 12. The throat for the Rumford must be 12 inches above the lintel while traditional construction only requires 8 inches.

    I hope that helps,

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  12. #12
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Two flues, one fireplace

    Quote Originally Posted by Ashley Eldridge View Post
    Vern, the acceptable rule is that for square liners or those with less than a 2-to-1 ratio (meaning the width of the tile is no more than twice the depth) the flue should be 1/10th the area of the fireplace opening. If the flue has a greater ratio it should be 1/8th the area of the fireplace. For round flues the flue should be 1/12th the area of the fireplace opening.

    One exception to that rule is the Rumford design. If the design features of that fireplace are followed the flue can be up to 1/20th the area of the fireplace opening. The simple formula for the Rumford is;
    if x designates the depth, then the width is 2x and the height is 3x.

    While the IRC specifies a minimum depth of a conventional firebox to be 20 inches, the Rumford can be as shallow as 12. The throat for the Rumford must be 12 inches above the lintel while traditional construction only requires 8 inches.

    I hope that helps,

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America
    Thanks Ashley, that's going in my referance folder.

    The beatings will continue until morale has improved. mgt.

  13. #13
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Two flues, one fireplace

    Quote Originally Posted by Ashley Eldridge View Post
    I hope that helps,

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America
    Yes, thanks for the info. Since fireplaces are built from the ground up, the mason here knew his opening size before the flues went up, eh?
    Quote Originally Posted by Evan Wray View Post
    The mason must have liked lots of draft on his fireplaces, he may have had a problem with draw in a heavily treed area previously. The real issues are the home owners heating dollars going up the chimney and the settling away from the house which may have stopped.
    I've posted a few more pics. What is your opinion of this fireplace?
    Quote Originally Posted by Evan Wray View Post
    Anyway just wanted to say hi to John K. I used to be a southern Van. Islander also. Merry green Christmas from the city of snow and ice.
    Evan W. mason ,Internachi member.
    We had a snow day at the end of November, cold one this year. I'd rather just watch it build up on the mountains. At least you guys can escape to the Mall.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  14. #14
    Evan Wray's Avatar
    Evan Wray Guest

    Default Re: Two flues, one fireplace

    It's got a lot of issues some money is going to be need spent on it. Hopefully it has stopped settling ,don't see any damage on the inside. There are mud jacking companies in Edmonton don't recall seeing any on the Island. Good luck.

    Evan Wray


  15. #15
    Ashley Eldridge's Avatar
    Ashley Eldridge Guest

    Default Re: Two flues, one fireplace

    Quote Originally Posted by John Kogel View Post
    Yes, thanks for the info. Since fireplaces are built from the ground up, the mason here knew his opening size before the flues went up, eh?
    I've posted a few more pics. What is your opinion of this fireplace?
    We had a snow day at the end of November, cold one this year. I'd rather just watch it build up on the mountains. At least you guys can escape to the Mall.
    John, the mason should know what size the opening will be and have a clear vision of how the chimney will be built to support it. That includes a proper foundation and flue sizing. You clearly have some settling issues here. The chimney pulling away from the house is never a good sign. Overall it looks like minimalist construction to me based on the block construction. The foundation is the most likely suspect. Whe images show me the chimney, I suspect the fireplace and remaining construction details will show similarly marginal to poor design and construction, but that is where many of the defects will be visible, from inside the structure.

    Ashley Eldridge
    Chimney Safety Institute of America
    Director of Education
    Chimney Safety Institute of America


  16. #16
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Two flues, one fireplace

    Thanks, guys. I described what you see here with lots of pics. There were other issues, electrical and plumbing. My clients walked away.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  17. #17
    Evan Wray's Avatar
    Evan Wray Guest

    Default Re: Two flues, one fireplace

    Good decision