Can a gas stove top be butted up to a refigerator? Looks to me that the outside of refigerator would melt.
Similar Threads:
-
12-23-2010, 06:06 AM #2
Re: Gas Stove top and Refrigerator
Doesn't sound like a good idea, but you will need to check with the stove/ refrigerator manufactures to see if they recommend against it.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
12-23-2010, 06:47 AM #3
Re: Gas Stove top and Refrigerator
some manufacturers do have zero clearance gas range/cook top...refer to install instructions whenever in doubt
anything less than 6" gets noted that the adjoining appliance/cabinetry may encounter heat discoloration/deformation, all users should avoid contact with these surfaces and monitor during usage
an image with +120ºF or greater surface temp usually gets the point across because that number has been discussed as the onset of scald...not that it will necessarily cause material damage but it will cause pain/possible burn upon direct skin contact
badair http://www.adairinspection.com Garland, TX 75042
Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
life is the random lottery of events followed by numerous narrow escapes...accept the good
-
12-23-2010, 03:15 PM #4
Re: Gas Stove top and Refrigerator
I went to the GE site and randomly selected one gas range to view its installation instructions ( http://products.geappliances.com/Mar...e=49-85170.pdf ) and it states the clearance to the right wall is 6" minimum and to the left wall is 3" minimum (depending on if there is a wall on the right, the left, or both sides).
-
12-23-2010, 03:50 PM #5
Re: Gas Stove top and Refrigerator
It is also quite common to find lateral (side) clearance requirements for refrigerators, even if allowed to be abutted against cabinetry or a sidewall - distances from HEAT generating sources is generally found (although you may have to hunt for it burried in otherwise ambiguous language or a note to a diagram).
NFPA 54 (aka its ANSI standard number referenced by the gas appliance manufacturer, if more stringent not specified by local code or in the manufacturer's instructions) also provides clearances from the burners to combustibles, etc. of the cooktop, grill, or range.
For the most part, generally refrigerator/freezer door gaskets don't pass the flame/smoke spread indices or metal guard thicknesses specified for close proximity to open flame burners, etc. Generally sidewalls of refrigerators are powder/electro-painted, not enameled steel, or high temp lum. paint, and of thinner guage metal and are trimmed in plastics, ABS often utilized, and styreen insulation for the freezer compartment at sidewalls.
Last edited by H.G. Watson, Sr.; 12-23-2010 at 04:01 PM.
-
12-24-2010, 08:47 AM #6
Re: Gas Stove top and Refrigerator
================================================== ====
True, but the 3" and 6" is the clearance to COMBUSTIBLES, adjacent to the rangetop. As long as the side of the fridge isn't plastic, or an old wooden ice box, should be fine.
OK, but what does the fridge manual say? I followed Jerry's link and checked a random GE refrigerator:
Allow the following clearances for ease of installation, proper air circulation and plumbing and electrical connections.• Sides 3/4" (19 mm) • Top 1" (25 mm) • Back 1" (25 mm)
We'd probably all agree that it's not the best arrangement, for all sorts of reasons, but sometimes it's unavoidable in a small kitchen. Just keep that side clearance per the fridge manual
-
12-24-2010, 12:49 PM #7
Re: Gas Stove top and Refrigerator
So, it is your opinion the the foam inside the refrigerator is not combustible?
And that the paint on the refrigerator will withstand 200 degrees F?
And that the rubber door gaskets are not combustible and can withstand 200 degrees F?
You did see this in that installation instructions, didn't you: "Make sure that wall coverings around the range can withstand heat generated by the range up to 200 degrees F."?
The side of the refrigerator becomes 'the wall' and needs to meet that temperature requirement ... at that 3" and 6 clearance.
If you want to reduce that stated required clearance, you would then go to the IRC and to Table G2409.2 Reduction of Clearances with Specified Forms of Protection. That 6" and 3" clearance can then be reduced to 2" if you install a 0.024-inch (nominal 24 gage) sheet metal with ventilated airspace, the ventilated air space is 1" minimum, leaving you at the same 3" for the 3" side.
It is not just as easy as saying 'Oh, the refrigerator has metal sides,', which is what H. G. was pointing out.
So you disregard the clearances shown for the refrigerator and go with those shown for the ranges as "the most restrictive shall apply".OK, but what does the fridge manual say? I followed Jerry's link and checked a random GE refrigerator:
Allow the following clearances for ease of installation, proper air circulation and plumbing and electrical connections.• Sides 3/4" (19 mm) • Top 1" (25 mm) • Back 1" (25 mm)
-
05-15-2011, 12:17 PM #8
Re: Gas Stove top and Refrigerator
refrig or stove needs moved always go one better then the code