Results 1 to 4 of 4

Thread: Missing ground?

  1. #1
    Join Date
    Jul 2010
    Location
    NC
    Posts
    122

    Default Missing ground?

    Main panel at today's inspection, single family home, 4/0 aluminum with 200 amp breaker. No wire at the ground bus on top. Is this proper. Also, I could not locate the grounding electrode at the exterior below the meter.

    Your comments are appreciated.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Joseph Stevens's Avatar
    Joseph Stevens Guest

    Default Re: Missing ground?

    Hi Sidney

    Sounds like you have basically answered your own questions. Should have 6ga. copper leaving panel going to ground rods. Also should be connected to water line if it is metallic.


  3. #3
    Roger Frazee's Avatar
    Roger Frazee Guest

    Default Re: Missing ground?

    Quote Originally Posted by sidney alstad View Post
    Main panel at today's inspection, single family home, 4/0 aluminum with 200 amp breaker. No wire at the ground bus on top. Is this proper. Also, I could not locate the grounding electrode at the exterior below the meter.

    Your comments are appreciated.
    If this is the service equipment then you should only have 3 wires from the utility feeding single phase 120/240 the panel .. the utility does not bring a ground into the home from the transformer.
    So .. no .. an equipment ground from the utility will not be present. It's normal.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Missing ground?

    Quote Originally Posted by Joseph Stevens View Post
    Should have 6ga. copper leaving panel going to ground rods.
    Quote Originally Posted by Roger Frazee View Post
    If this is the service equipment then you should only have 3 wires from the utility feeding single phase 120/240 the panel .. the utility does not bring a ground into the home from the transformer.
    So .. no .. an equipment ground from the utility will not be present. It's normal.
    Both of the above are correct ... depending on the AHJ.

    Some AHJ will require the grounding electrode conductor to be connected where they can see the connection - which means in the service equipment.

    Some AHJ allow the grounding electrode conductor to be connected within the meter can, thus you will not see it in the service equipment.

    Additionally, there are some real derating issues apparent, unless those raceways going out the top of the service equipment are less than 24" long (they are likely longer than 24", which creates the derating problem).

    Additionally, each of the NM cables are required to be secured to the enclosure, which (obviously) cannot be done when installed in raceways as shown (there is an exception to this also, but that exception does not apply to this non-surface mounted enclosure).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •