A question about Multi-branch circuits
Ok I have seen the classic disposal and dishwasher multi-branch circuits on split-wired receptacles on the same outlet. Today I saw half the house wired this way and the single pole breakers were not tied together, I wrote it up and recommend further review. However I just want to bounce what I saw in the panel to make sure I was correct. Here is the situation, as an example they had one breaker feeding outlets in a bedroom and the second breaker feeding hall lights. A single Romex cable with two hots, one neutral and a ground.
My question are:
1. They are still multi-branch circuits which need to be tied together even though they are feeding more than one outlet and more than one light fixture, correct?
2. In general do you see any problem with the neutral with the way they ran the circuits?
3. Is there anything that I am missing?
Similar Threads:
-
01-31-2011, 07:47 PM #2
Re: A question about Multi-branch circuits
The handle tie requirement for multiwire branch circuits was new in the 2008 NEC. If the panel was installed under an earlier code (regardless of actual installation date) then IMO it cannot be considered a "defect". It can certainly be called for evaluation, but if I were to look at it I would write it up as perfectly code complaint and safe.
Nope. Been fine and complaint for MANY years.
-
02-01-2011, 06:07 AM #3
Re: A question about Multi-branch circuits
Might be worth adding here that if the disposer and dishwasher are on the same receptacle and supplied by individual breakers that a handle tie would be required. That rule has been around a long time.