    Default Stairway lighing

    Last edited by RobertSmith; 12-20-2007 at 01:52 PM.
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: Stairway lighing

    There is a lumens rating that must be met for stairs. I don't know it offhand. I think Scott P. posted it last year, and he may still have it.

    Jim Robinson
    New Mexico, USA

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Stairway lighing

    From the IRC. (underlining is mine)
    - R303.6 Stairway illumination.
    All interior and exterior stairways shall be provided with a means to illuminate the stairs, including the landings and treads. Interior stairways shall be provided with an artificial light source located in the immediate vicinity of each landing of the stairway. For interior stairs the artificial light sources shall be capable of illuminating treads and landings to levels not less than 1 foot-candle (11 lux) measured at the center of treads and landings. Exterior stairways shall be provided with an artificial light source located in the immediate vicinity of the top landing of the stairway. Exterior stairways providing access to a basement from the outside grade level shall be provided with an artificial light source located in the immediate vicinity of the bottom landing of the stairway.

    - - - Exception:
    An artificial light source is not required at the top and bottom landing, provided an artificial light source is located directly over each stairway section.

    - - R303.6.1 Light activation.
    Where lighting outlets are installed in interior stairways, there shall be a wall switch at each floor level to control the lighting outlet where the stairway has six or more risers. The illumination of exterior stairways shall be controlled from inside the dwelling unit.

    - - - Exception:
    Lights that are continuously illuminated or automatically controlled.