    Southwest US
    Default Double traps, what is the implication?
    House today had a 3-bay kitchen sink. The left sink was triple trapped, the right double trapped, center and disposal were OK. I know this is wrong but couldn't come up with any good reason to explain to the client except "it isn't code". What are the possible implications? Only thing I could think is that it may clog more easily.
    James Duffin's Avatar
    James Duffin Guest
    Default Re: Double traps, what is the implication?
    You got a picture of all of them traps?
    [quote=Benjamin Thompson;161219]The left sink was triple trapped, the right double trapped, center and disposal were OK.{/quote]
    One trap fed into the next trap which fed into the next trap?
    Traps won't scour and self-clean as designed, leading to traps clogging up and back-up into sinks/disposer/dishwasher.
    Southwest US
    Not a very good pic as you can't see the third trap behind the disposal on the main drain line, It's down behind the Coca-Cola bottle. So. right sink 3 traps, center sink and disposal 1 trap, left sink 2 traps.
    James Duffin Guest
    Here is what the NC Plumbing Code Says:
    1002.1 Fixture traps. Each plumbing fixture shall be separately
    trapped by a water-seal trap, except as otherwise permit- Ited by this code. The vertical distance from the fixture outlet to
    the trap weir shall not exceed 24 inches (610 mm) and the horizontal
    distance shall not exceed 30 inches (610 mm) measured
    from the centerline of the fixture outlet to the centerline of the
    inlet ofthe trap. The height ofa clothes washer standpipe above
    a trap shall conform to Section 802.4. A fixture shall not be
    double trapped.
    Exceptions:
    1. This section shall not apply to fixtures with integral
    traps.
    2. A combination plumbing fixture or up to three similar
    fixtures is permitted to be installed on one trap, provided
    that one compartment is not more than 6 inches
    (152 mm) deeper than the other compartment and the
    waste outlets are not more than 30 inches (762 mm)
    apart
    Bryan Dilworth's Avatar
    Bryan Dilworth Guest
    Double traps cause slow drainage. The air between the traps becomes compressed as the water drains.