Results 1 to 2 of 2
-
04-08-2011, 02:16 AM #1
Gas supply lines for gas log fireplace
Just ran into this yesterday. Heat-n-glo gas log unit installed in the corner of a basement.
Two flex lines joined together from steel gas pipe are supplying the unit. Wasn't sure how to call or phrase this defect. Any suggestions?
Similar Threads:Last edited by Ron Poteet; 04-08-2011 at 02:18 AM. Reason: mispelled word
-
04-08-2011, 03:03 AM #2
Re: Gas supply lines for gas log fireplace
IRC G2422.1.2.1 (411.1.3.1) Maximum length. Connectors shall have an overall length not to exceed 3 feet (914 mm), except for range and domestic clothes dryer connectors, which shall not exceed 6 feet (1829 mm) in overall length. Measurement shall be made along the centerline of the connector. Only one connector shall be used for each appliance.
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com