    I can't put my finger on it, but the attached photo doesn't look right to me. Is this acceptable or is my instinct right?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Lou Romano's Avatar
    Lou Romano Guest

    Default Re: Overhead Wiring

    Did you post this as a joke?

    This is NOT acceptable in any way! No way POCO hooked this up, it was done by someone without a conscience.

    Where's the weatherhead?
    Where's the Main disconnect?
    Where's the meter?

    This needs immediate attention from a licensed electrician.


  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Overhead Wiring

    Is that the utility overhead or a feeder going to an outbuilding?

    If that is the overhead supplying the electric to the house it would be very hard to comply with the code requirement to keep the unfused service conductors as short as practical after entering the building.

    Can you supply more info?

    All answers based on unamended National Electrical codes.

  4. #4
    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest

    Default Re: Overhead Wiring

    This is the main overhead wiring to the home. It runs about five or six feet in the attic and then drops down the interior wall to the meter.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Overhead Wiring

    Quote Originally Posted by Stephen G Sheldon View Post
    This is the main overhead wiring to the home. It runs about five or six feet in the attic and then drops down the interior wall to the meter.
    That is completely wrong.

    The meter is inside the house? I suspect the house has had an addition added to it and that the meter was originally on the outside wall of the house.

    An electrical contractor needs to make corrections as soon as possible.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest

    Default Re: Overhead Wiring

    The meter is on the outside. Its just that the main wiring must runs down the inside of the wall where it then attaches to the meter. There is no conduit visible on the exterior of the home. This is a house built in 1957 if that helps. I apologize if I;m not making this very clear.


  7. #7
    Join Date
    Mar 2007
    Location
    georgia
    Posts
    112

    Default Re: Overhead Wiring

    Stephen, I see you are from atlanta with that said a lot of services in houses of that era were installed by Georgia Power. They would run the unprotected cable thru the structure down an exterior wall to the meter then continue to the service panel. They would put stickers on the panel that said it was property of Georgia Power and had to repair and replace a lot of equipment thus they stopped this practice.

    With all that said electricians would copy their installation until the local jurisdictions corrected them and required overcurrent protection prior to the cable passing thru the structure.

    As for your picture it is missing the clamp on SEU type weather head but other than that it is typical for that era around here. Still not correct but typical.


  8. #8
    Join Date
    Feb 2009
    Location
    Southeast Virginia, Hampton roads
    Posts
    51

    Default Re: Overhead Wiring

    I've seen this several times. It's just antiquated wiring methods and I report it as such.