Results 1 to 17 of 17
Thread: Trac pipe by Omega Flex
-
05-13-2011, 06:33 AM #1
Trac pipe by Omega Flex
Anyone familiar with the installation instructions on this. I can't find an area which addresses penetration through metal into thehousing of a gas fireplace. This is a new condo hotel which was just completed. (Montage in Deer Valley)
Similar Threads:
-
05-13-2011, 07:17 AM #2
Re: Trac pipe by Omega Flex
Matt, I see that same type of install all the time beneath fireplaces. Some fireplace manufacturer install manuals call for black iron piping through the knockout location, some say refer to local codes. I'm not sure what Omega Flex calls for in this situation. When I run across it, I just recommend installing a rubber grommet around the line where it passes through through the knockout unless the fireplace installation manual is very specific about the type gas line material they require.
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
05-13-2011, 07:20 AM #3
Re: Trac pipe by Omega Flex
Found it. Page #41.
http://www.omegaflex.com/trac/techni...Omega_Flex.pdf
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
05-13-2011, 07:38 AM #4
Re: Trac pipe by Omega Flex
When it is necessary to installTracPipe
through sheet metal enclosures, such as
those commonly used in decorative gas
fireplaces, the manufacturer’s recommendation
is to leave the protective yellow
polyethylene jacket in place through the
sheet metal penetration. TheTracPipe
should be clipped to the building structurebetween the jacket and the enclosure.
at a suitable location outside the fireplace
to limit the amount of motion after installation.
If additional protection is required,
such as an installation with a source of
vibration (fan, etc.) which may cause
abrasion, then a short piece of floppy
conduit or PVC pipe may be used
So as long as there is a clip, which I can't see, its good to go
-
05-13-2011, 08:05 AM #5
Re: Trac pipe by Omega Flex
Matt, do they bond the CSST there? I seem to get a blank look from any plumber or electrician when I bring it up here. I have yet to find it bonded according to the manufacturer's instructions (usually Ward Flex here).
Jim Robinson
New Mexico, USA
-
05-13-2011, 12:41 PM #6
-
05-13-2011, 04:47 PM #7
Re: Trac pipe by Omega Flex
I get the blank look as well. I have to look, usually I see ward flex as well.
-
05-13-2011, 05:26 PM #8
Re: Trac pipe by Omega Flex
-
05-14-2011, 05:35 AM #9
-
05-14-2011, 05:34 PM #10
Re: Trac pipe by Omega Flex
I say not required. Recommended if there is a fan.
-
05-15-2011, 08:37 AM #11
Re: Trac pipe by Omega Flex
"Most gas fireplaces and gas logs (Refer to ANSI Z24.60) fall into the definition of fixed appliances which can be directly connected to TracPipe without the use of a flange mount fitting. The attachment is generally to the shut-off valve which may be located in the control area beneath the burner unit or at the side of the log set. TracPipe can be run into the lower control area for attachment without removal of the polyethylene jacket. In vented fireplaces, attachment to gas logs is best accomplished by removal of the jacket inside the fire box. This precludes direct flame contact with the polyethylene jacket. Stainless Steel melting temperatures (2000o F) are consistent with black iron."
-
05-15-2011, 04:59 PM #12
Re: Trac pipe by Omega Flex
The mfr. says you can connect directly to the appliance, which I have done many times and see no problem per se. However, you would have to remove the poly jacket to meet the stated clearances to combustibles whether factory built fireplace with vented logs or a gas appliance such as a direct vent. Too, you need a shutoff either within 6ft of the appliance or one that meets the three criteria: serves only that appliance, labelled, and readily accessible. It *should* have a sediment trap somewhere but fireplaces get special dispensation from the ICC as not mandatory within 6ft. With a basement, the better approach is simply incorporate a sed. trap with shutoff below the Fp that is 'readily accessible' and labelled.
Interesting perspective but I'm not sure any of the CSST mfrs. have tested their product passing through a factory built fireplace. The penetration into any fireplace should be sealed appropriately.
Keep the fire in the fireplace.
-
05-15-2011, 06:36 PM #13
Re: Trac pipe by Omega Flex
Bob,
Questions for you (we are out camping to - hopefully - watch the shuttle launch tomorrow morning and I do not have my codes on this computer):
- I thought the IRC did not require a sediment trap at all for illumination appliances such as clothes dryers, gas light, ranges, fireplaces, and the like.
- I thought the 6 feet was applicable to the shut off, not to the sediment trap.
-
05-15-2011, 07:19 PM #14
Re: traps, shutoffs and Fps
JP, hope the lauch goes well.
A sed trap is not *required* but recommended which is what I said. G2419.4 calls for the trap (when installed) to be located downstream of the appliance shutoff. G2420.5 requires shutoffs within 6 ft of the appliance, which puts the trap within 6ft. However since fireplaces are allowed to have shutoffs remote from the appliance, so too are the traps for them. However, it would still be a best practice to locate the trap as close as reasonably practical to the appliance where it can be accessed for inspection, service or attach as gas pressure manometer. Putting traps downstream of shutoffs is intended to provide a point to tap into the piping for a direct inlet gas pressure reading.
HTH,
Keep the fire in the fireplace.
-
05-16-2011, 06:30 AM #15
Re: Trac pipe by Omega Flex
In my opinion the real question is that the CSST will rub on the metal edges of that opening. Flex pipe is not allowed to penetrate opening at furnace, is this the same thing? I also never see the pipe grounded or bonded, I don't think they know how to. I have seen two installations in the last week where they ran the CSST through the clean out at exterior into firebox.
-
05-16-2011, 03:09 PM #16
Re: traps, shutoffs and Fps
Bob,
Gotcha, it was the way I was reading what you wrote that threw me off, I was thinking you were saying there was a code which specified that the sediment trap had to be within 6 feet - no but ... as you pointed out, the shut off has to be within 6 feet, and (of course) the sediment trap is downstream from the shut off, ergo "within 6 feet" ... excepting the fireplace location stuff.
I've got to try to remember that 'sediment trap within 6 feet' thing as I bet I can mess with some gas pipe installers minds ...
-
07-28-2011, 08:06 PM #17
Re: Trac pipe by Omega Flex
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
Bookmarks