    Just to make sure, there is no way to reduce the clearance to ceiling requirement using metal ceiling tiles correct?

    This unit has the standard 18" clearance requirement and as installed there is approximately 7" to the metal ceiling tile and 9 - 10" to the wood joists above.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Wood stove clearance to ceiling

    I'm not an authority on this, but I believe you are correct, that is not an approved way to install a wood burner.
    Changing the stove pipe to a double-walled pipe might be an option there, but I'd wait for the pros to make the call.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Wood stove clearance to ceiling

    Quote Originally Posted by Jon mackay View Post
    Just to make sure, there is no way to reduce the clearance to ceiling requirement using metal ceiling tiles correct?

    This unit has the standard 18" clearance requirement and as installed there is approximately 7" to the metal ceiling tile and 9 - 10" to the wood joists above.
    If it is only 7" from the ceiling then it does not meet the proper clearance requirement. Even with allowable reduction measures it does not meet the distance. The closest distance with proper reduction measures would be 9" from the ceiling.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    MARVIN TOWNSEN's Avatar
    MARVIN TOWNSEN Guest

    Default Re: Wood stove clearance to ceiling

    Wouldn't that be considered a non-combustible surface with a 1" air gap that would reduce clearances?


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Wood stove clearance to ceiling

    I suspect you guys are referring to the table for reduction of clearances in the IRC Mechanical section.

    That table is not to be used for reduction of clearances with a minimum clearance of 12 inches, nor is that table to be used for reduction of clearances greater than 12 inches to less than 12 inches.

    I.e., if the clearance is specified at 12 inches, the clearance is 12 inches (that table cannot be used to reduce that 12 inches).

    I.e., if the clearance is specified at 18 inches, the table can only be used to reduce the clearance to 12 inches.