06-15-2011, 03:16 PM #1
Plastic Main Service Pipe
I was at a house this afternoon and saw that the main water service line entering the home was a blue plastic pipe. It looked like PEX to me. The pipe was grouted all around where it penetrated the wall. I was thinking that the pipe should be in a protective sleeve and not grouted but caulked as it leaves the wall. The builder says the pipe is CTS and designed to be used through concrete walls and not repairs are necessary. Who is right?
Similar Threads:
-
06-15-2011, 03:53 PM #2
Re: Plastic Main Service Pipe
Pics?
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
06-15-2011, 04:12 PM #3
Re: Plastic Main Service Pipe
CTS is CPVC pipe. Try this site it should help you. I see it from time to time and most of the time it is passed through a larger section of PVC pipe that acts as a sleeve and allows for thermal expansion of the pipe. http://www.harvel.com/downloads/spec-hydroking.pdf
-
06-15-2011, 04:50 PM #4
Re: Plastic Main Service Pipe
IRC 2606.3 says it has to be sleeved.
Have him show you in the code where there is an exception.
"The Code is not a peak to reach but a foundation to build from."
-
06-15-2011, 05:40 PM #5
Re: Plastic Main Service Pipe
And the sleeve is required to be two sizes larger.
The annular space between the sleeve and the foundation wall would be grouted and sealed tightly. The annular space between the inner pipe and the outer sleeve would also need to be sealed, but with a sealant which is compatible with the material - not all sealants are compatible with CPVC.
-
06-15-2011, 06:17 PM #6
Re: Plastic Main Service Pipe
Hers is what the NC plumbing code says.....
305.5 Pipes through or under footings or foundation walls.Any pipe that passes within 12 inches (305 mm) under a footingfooting (refer to Section 307)
or through a foundation wall shall be provided with a relieving
arch, or a pipe sleeve pipe shall be built into the foundation
wall. The sleeve shall be two pipe sizes greater than the pipe
passing through the wall. Piping shall not be run under pier