    Ran into this today. Feeder cables from the service equipment to the laundry area panel are run underground. While the wire insulation designation indicates the wires are rated for water, I was under the impression that buried electrical cables need to be UF.

    Am I correct?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Buried SER Type XHHW cable


    C&P.....


    Section 338.12 has been added to the 2008 NEC and covers uses not permitted for both Type SE and Type USE cables. It states that Type SE cable cannot be used where subject to physical abuse, unless adequately protected, and can never be installed in an underground installation, with or without a raceway.



  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Buried SER Type XHHW cable

    Also, underground cables installed under buildings shall be in a raceway.

    Cables installed directly in the ground shall also be listed for direct burial, not that it matters for under a building (see above).

    Really don't see anything correct about that installation.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Buried SER Type XHHW cable

    Thanks Jerry & James,

    That was my thought, but I was unable to find it.

    "But it passed building inspection!"

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Buried SER Type XHHW cable

    Quote Originally Posted by Gunnar Alquist View Post
    "But it passed building inspection!"
    Nah ... the inspector "just didn't see it".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Buried SER Type XHHW cable

    How long before the EGC turns to toothpaste? IMO moisture will wick into the cable assembly & the AL can turn into a toothpaste like substance. Underground is considered a wet location.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Buried SER Type XHHW cable

    Quote Originally Posted by Rollie Meyers View Post
    How long before the EGC turns to toothpaste? IMO moisture will wick into the cable assembly & the AL can turn into a toothpaste like substance. Underground is considered a wet location.
    "Underground is considered a wet location." As is the inside of a raceway underground.

    And AL is used in direct burial cables and in raceways underground.

    Basically, there is nothing correct about that installation as shown in the photos, and the more information we get, the worse the work will likely get.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Buried SER Type XHHW cable

    Quote Originally Posted by Jerry Peck View Post

    Basically, there is nothing correct about that installation as shown in the photos, and the more information we get, the worse the work will likely get.

    Sad to say both statements are true.