Results 1 to 11 of 11
Thread: GFCI breaker for multiple rooms
-
07-14-2011, 08:08 PM #1
GFCI breaker for multiple rooms
I inspected a home today where a 20A GFCI breaker served the bathroom, the bathroom fan, the bath vanity lights and the recessed lights in two other rooms.
Is this OK to do or is this a code issue?
Similar Threads:
-
07-14-2011, 08:36 PM #2
Re: GFCI breaker for multiple rooms
That is okay. It is one of the options.
-
07-14-2011, 10:38 PM #3
Re: GFCI breaker for multiple rooms
This is a copy & paste from the 2008 NEC 210.11(C) (3).
(3) Bathroom Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one 20-ampere branch circuit shall be provided to
supply bathroom receptacle outlet(s). Such circuits shall
have no other outlets.
Exception: Where the 20-ampere circuit supplies a single
bathroom, outlets for other equipment within the same
bathroom shall be permitted to be supplied in accordance
with 210.23(A)(1) and (A)(2).
FPN: See Examples D1(a), D1(b), D2(b), and D4(a) in
Annex D.
The issue of the OP's post would depend on the NEC in effect at the time of the work was performed, it does not comply w/ the 2008, & nor does it comply w/ the 2005 which is when that change first came into the NEC, if that was done before those 2 editions then it's fine.
-
07-15-2011, 03:18 PM #4
Re: GFCI breaker for multiple rooms
-
07-15-2011, 03:54 PM #5
Re: GFCI breaker for multiple rooms
All answers based on unamended National Electrical codes.
-
07-15-2011, 04:08 PM #6
Re: GFCI breaker for multiple rooms
-
07-15-2011, 04:10 PM #7
Re: GFCI breaker for multiple rooms
Originally Posted by Rollie Meyers
Jerry,
The way I read this is that the bathroom circuit can have no other outlets. Doesn't that mean that lights in other rooms cannot be supplied by the bathroom cicuit?
-
07-15-2011, 04:15 PM #8
Re: GFCI breaker for multiple rooms
Ken
It's in the execption
Exception: Where the 20-ampere circuit supplies a single
bathroom, outlets for other equipment within the same
bathroom shall be permitted to be supplied in accordance
with 210.23(A)(1) and (A)(2).
FPN: See Examples D1(a), D1(b), D2(b), and D4(a) in
Annex D.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
07-15-2011, 04:26 PM #9
Re: GFCI breaker for multiple rooms
Ken
I misread your question.
You are correct.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
07-15-2011, 05:38 PM #10
Re: GFCI breaker for multiple rooms
Ken,
No, think "outlets" and not "receptacle" outlets - lighting outlets are also "outlets".
All the other electrical "outlets" in the same bathroom may be on that same 20 amp circuit.
What I missed when I read your post was the last part about "and the recessed lights in two other rooms" - I read it as "and the recessed lights" ... I completely and totally missed the very critical "in two other rooms" part.
The 20 amp bathroom receptacle outlet circuit may supply as many receptacle outlets in as many bathrooms as you want ... or ... one 20 amp circuit may supply ONE bathroom and as many outlets in that bathroom as you want.
-
07-16-2011, 04:37 PM #11



Reply With Quote