Results 1 to 5 of 5
			
		Thread: Ground round @ meter base
- 
	07-30-2011, 06:30 AM #1 Ground Rod @ meter base Ground Rod @ meter baseInspected this house today, built in the early 80's. This house had the ground rod at meter base up by the rod about 100 yards from the from of the house. The main wire went underground about 120 yards to the the panel, with no ground at the main panel just the 1 at the road. Is this acceptable??? 
 Similar Threads:Last edited by Sam Morris; 07-30-2011 at 06:32 AM. Reason: Ground Rod 
 
- 
	07-30-2011, 07:42 AM #2 Re: Ground round @ meter base Re: Ground round @ meter baseDo you have a photo of this setup and one of inside of the panel? 
 
 
- 
	07-30-2011, 08:57 AM #3 Re: Ground round @ meter base Re: Ground round @ meter baseAre you refering to a manufactured home connection from a pedestal? 
 
 Are you suggesting there was no bonding at the equipment?
 
 There should be more than one conductor ("wire") from the equipment. How many conductors are present? Is there a main disconnect at this "meter" location? Protection? (main power feeder, service lateral, etc.).
 
 Was there any other metalic or return path between these two structures?
 
 Are you aware that there are more than one type of electrode ("made" or otherwise), i.e. there are other options besides "rods" which can be used in a grounding electrode system.
 
 
- 
	07-30-2011, 10:41 AM #4
 
- 
	07-31-2011, 08:12 AM #5 Re: Ground round @ meter base Re: Ground round @ meter baseThere are double taps on the top two breakers. There are neturals that cross over the panel just above the top breakers. That is a target rich environment. Sparky needs to come out and fix lots of stuff. Have him fix any missing ground at the same time. 
 "The Code is not a peak to reach but a foundation to build from."
 


 
 
						
					 
					
					
 
				
				
				
					 Reply With Quote
  Reply With Quote Originally Posted by H.G. Watson, Sr.
 Originally Posted by H.G. Watson, Sr.
					

Bookmarks