Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Check those CSST connections

    I found this today on a warranty inspection. The CSST was too short for the application, it had been kinked and it was also not protected. To top it off it was starting to pull out of the fitting.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Check those CSST connections

    Scott,

    When are you going to quit kinking gas lines and stuff ... just so you can write them up?



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    dick whitfield's Avatar
    dick whitfield Guest

    Default Re: Check those CSST connections

    I would have fixed it and checked for leaks.....N/C!


  4. #4
    Tim Moreira's Avatar
    Tim Moreira Guest

    Thumbs down Re: Check those CSST connections

    ??????????

    Liability, liability, liability

    ??????????

    And after you leave, what happens if...............


  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Not CSST

    What was pictured is technically a "flexible applance connector" listed to ANSI Z21.24. The basic application here is acceptable to the flex mfr. as long as it is not exposed where it could be expected to get damaged. It depends on what is going on to the side of that WH where the folding chair is. Personally, I would have run 1/2" CSST from the shutoff to the sediment trap/ valve.

    Keep the fire in the fireplace.