Results 1 to 6 of 6
Thread: Any idea why this box is here?
-
08-19-2011, 01:45 PM #1
Any idea why this box is here?
I didnt open it. These 100 degree days are killers.
This is on a 240V circuit to an AC condensing unit (1 of 2 units on a 2 story house).
Similar Threads:
-
08-19-2011, 02:59 PM #2
-
08-19-2011, 03:28 PM #3
Re: Any idea why this box is here?
Thanks Ted. I kind of figured the conductors were too short or something so they spliced. Other than the connectors of the box not fully set, do you see anything glaringly wrong with doing this?
-
08-19-2011, 05:39 PM #4
Re: Any idea why this box is here?
Other than it is about time to change the insulation out and that left connection looks rather bent up and may not be sealing that connector as it should to keep dry. Also. Who knows what it looks like inside. It may be OK or could be a dangerous connection if done wrong.
I thnk I would have mounted a box on nthe wall and then ran a new lead to the unit from that box as in a disconnect. That would cancel out all those questions.
-
08-19-2011, 08:01 PM #5
Re: Any idea why this box is here?
Let's see, the junction box is not securely mounted, one connector at least is providing no "weather resistance" whatsoever, the flexible conduit is barely secured by very old duct-tape, and the box has been secured in a position which makes it impossible to remove the cover-plate.
That's all I can see right now, dinner is ready.
-
08-20-2011, 06:52 PM #6
Re: Any idea why this box is here?
This appears to be a pull box, not a junction box. The liquid tight fitting on the right is not properly installed.
Randall Aldering GHI BAOM MSM
Housesmithe Inspection
www.housesmithe.com



Reply With Quote

Bookmarks