Disconnect question
Is there an issue with the / a disconnect attached to the /a condenser cabinet or FAU cabinet?
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-01-2011, 09:23 PM #2
Re: Disconnect question
Depends on where it is attached to the cabinet.
It is not allowed to be attached to any panel which is a removable service panel, starting with the actual service area cover, and includes any other panel removal for service - what panels would you remove to replace the coil if you were going to replace it?
-
12-01-2011, 09:30 PM #3
Re: Disconnect question
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-01-2011, 10:12 PM #4
Re: Disconnect question
Hi Mark
NEC 2011
440.14 Location. Disconnecting means shall be located
within sight from and readily accessible from the air conditioning
or refrigerating equipment. The disconnecting
means shall be permitted to be installed on or within
the air-conditioning or refrigerating equipment.
The disconnecting means shall not be located on panels
that are designed to allow access to the air-conditioning or
refrigeration equipment or to obscure the equipment nameplate(
s).
-
12-01-2011, 10:15 PM #5
Re: Disconnect question
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-02-2011, 05:16 AM #6
Re: Disconnect question
Most RTU's have locations that will allow access w/o interference.
Most residential ground unit types do not. IME
The FMC fed unit in the previous post pic doesn't appear to have a grounding conductor. I run across this all the freaking time. A unit is replaced using the existing whip w/o an EGC.
In Michigan at least, FMC and even LT-FMC is no longer considered a EGC regardless of length.
Where is the installation in question located?
Ditto on 'don't cover the nameplate' Jerry.
Further rant.... don't place the A/C condenser if front of the stinking disconnect!
-
12-02-2011, 08:23 AM #7
Re: Disconnect question
Here's a pic of that disco.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-02-2011, 08:54 AM #8
Re: Disconnect question
NO EGC ran inside the FMC as Bob said , I'd recommend one. Also big knockout missing that needs to be closed. I once took the access cover off one of these on a rooftop at Ford and was staring one of the biggest paper wasp nests I've ever seen face to face. About the time I went the wasps went and the fight was on....
I'm in a hurray this morning Marc so I'll let Bob expand on the EGC reasoning vs just using the FMC and another issue appears to be the lock ring in the upper right.
-
12-02-2011, 09:09 AM #9
Re: Disconnect question
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com