Dedicated single garage receptacle and GFCI
While inspecting a home this week constructed in 2005, I noticed that two single receptacles in the garage were on their own dedicated 20 AMP circuit (one to operate a golf cart charger and the other for a refrigerator). In refering back to NEC section 210.8, there is no GFCI exception for this type of circuit. A local electrician advised that this is a correct exception but could not remember the NEC section. Can anyone advise the correct NEC section which deals with single receptacles in a garage as an exception to the GFCI requirement?
Similar Threads:
-
01-17-2012, 06:39 AM #2
-
01-17-2012, 07:09 AM #3
Re: Dedicated single garage receptacle and GFCI
Rollie, thanks for your quick reply. However, what I was looking for was the exception that did not deal with appliances that are not frequently moved (NEC 210.8(A)(2) exception 2) such as a hand held golf cart charger. Is there another exception dealing with the single receptacles on a dedicated circuit that is not contained in 210.8?
-
01-17-2012, 07:50 AM #4
Re: Dedicated single garage receptacle and GFCI
Ken mentioned garage door opener receptacles, in the 2011 NEC if a GFCI receptacle is installed in the garage ceiling it must be readily accessible. This means that if you cannot press the test button while standing on the floor it's now a violation. I can just reach the buttons on an 8' ceiling, a short inspector might only be able to reach a receptacle installed at 7'.

One other note, the State of New Jersey has a code amendment to keep the exceptions that appeared in the 2005 NEC.
-
01-17-2012, 11:12 AM #5
-
01-18-2012, 08:01 AM #6
-
01-18-2012, 08:34 AM #7
Re: Dedicated single garage receptacle and GFCI
Here's the definition from article 100 of readily accessible. Can you explain how a device at 7' does not meet the definition?
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.
-
01-18-2012, 08:54 AM #8
Re: Dedicated single garage receptacle and GFCI
I have a guy (not very tall) that helps me on my rentals.
The other day we were painting, I told him to get the ladder off the turck and remove the covers off the light switches.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
01-18-2012, 04:03 PM #9
Re: Dedicated single garage receptacle and GFCI
-
01-19-2012, 05:13 AM #10
Re: Dedicated single garage receptacle and GFCI
-
01-19-2012, 05:17 AM #11
-
01-19-2012, 05:47 AM #12
Re: Dedicated single garage receptacle and GFCI
The reason the exception was removed form the NEC is because people were unplugging the equipment from the single receptacles and then using portable tools in the garage or outside without GFCI protection. IMO that does increase the likelihood of a lethal electric shock.
-
01-19-2012, 05:47 AM #13
Re: Dedicated single garage receptacle and GFCI
And the village idiot will promptly plug an extension cord into the same receptacle to prevent their favorite power tool from tripping the GFCI every time they use it. Same deal with formerly dedicated appliance receptacles where the original owner that got rid of a freezer, or a new owner without one, uses as a general use receptacle - they now have a non GFCI receptacle in the garage.
I'm all for laws that would require residences for sale to have GFCIs installed to current code.
Come on Petey - you HAD to know the rule change had nothing to do with properly grounded door openers, right?
Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
-
01-19-2012, 06:02 AM #14
Re: Dedicated single garage receptacle and GFCI
If a freezer/refrig (not easily movable appliance) was plugged into the outlet instead of the golf cart or in addition to the golf cart then there would not be an issue, correct?
-
01-19-2012, 06:22 AM #15
Re: Dedicated single garage receptacle and GFCI
General question. Though I do not think it makes a difference.
Since the home was built in 2005 and jurisdictions implement newer NEC at different times, would the 2003 NEC make any difference in this discussion?
((((((I admit for being a little lazy for not looking it up on my own.))))))) :-)
-
01-19-2012, 06:46 AM #16
Re: Dedicated single garage receptacle and GFCI
Same requirements in the 2002 edition as in 2005. The trend is to eliminate the exceptions to GFCI requirements, in the future IMHO, they will be like the requirements for commercial kitchens where all 120V 15 & 20A cord & plug connected equipment has to have GFCI protection w/ NO exceptions.



Reply With Quote