Old electrical Panels
Hi guys,
I was inspecting 58 years old house last week and the electrical panel didn't have "main disconnect switch".
I'm looking for a good article about old panels and what we should exactly inspect when we face them?
Thanks,
Eric
"Archway Home Inspections"
Similar Threads:Last edited by Eric Farjoo; 02-21-2012 at 11:47 PM. Reason: Add a picture of meter
-
02-21-2012, 04:19 AM #2
Re: Old electrical Panels
read it and weep! if you didn't make you're client aware of this you were not doing you're job
Federal Pacific Electric FPE Stab-Lok Panel Circuit Breaker Hazard, Repairs, Electrical Panel Replacement Electricians Directory for Stab-Lok Repairs
-
02-21-2012, 05:24 AM #3
Re: Old electrical Panels
Given that there are no known recalls in Canada other than defective 15 amp breakers back in 1996 and 1997 in which case these breakers were replaced free of charge, Canada does not appear to have had the same issues as state side.
And since I have seen quite a few of these panels over the years in Ontario, and have received no other advice from fellow inspectors, nor electrical inspectors, nor electricians the problem state side is not a problem up here.
My suggestion is for you to have your client have an electrical inspection prior to close of title to ensure it is safe.
Did you remove the cover plate?
As to the other photos that is an old bell telephone type transformer, typical in older housing.
-
02-21-2012, 07:37 AM #4
Re: Old electrical Panels
Is that a split buss panel?
-
02-21-2012, 10:42 AM #5
-
02-21-2012, 12:21 PM #6
Re: Old electrical Panels
Ray is correct, the Federal panels built in Toronto, Canada, have a different history than the FPE problems that occurred stateside. Also, we don't see the narrow wafer breakers here, so that problem of two prongs in one slot does not occur.
( I see this one is a Federal Electric, not Pacific or Pioneer. It is an old split buss piece of crap.)
Federal Pioneer panels are probably the most common panel that I see up here. These are the newer ones, owned by Schneider Electric.
Nevertheless, any breaker panel of that early vintage, over 40 years old and old breakers installed, should be replaced. You can say it needs to be inspected carefully by an electrician and pass it off that way, but I just say it needs to be replaced.
Point #2, no main breaker, no matter what the brand of panel, is another reason for replacement. The service as a whole will need to be upgraded.
Re: removing the cover. If it's an old one and the breakers flop around when you loosen the cover, tighten the screws back up and call for it to be inspected by an electrician. There are some models that have the breakers held against the covers with springs. Those are deadly panels. The newer ones are easy to inspect and the breakers are pretty snug in the bus bars as a rule.
Last edited by John Kogel; 02-21-2012 at 12:29 PM.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
02-21-2012, 01:45 PM #7
Re: Old electrical Panels
Eric,
Dumb question, but did you check for the main disconnect at the meter? Thats what I have found around here with some of the FPE's.
-
02-21-2012, 02:18 PM #8
Re: Old electrical Panels
Photo #3 is an old telephone fused primary protector. Info on these devices can be found in NEC section 800.90.

-
02-21-2012, 02:54 PM #9
Re: Old electrical Panels
-
02-21-2012, 03:08 PM #10
Re: Old electrical Panels
-
02-21-2012, 04:04 PM #11
Re: Old electrical Panels
-
02-21-2012, 11:55 PM #12
Re: Old electrical Panels
Thank you very much everybody, especially you Ray for all these good info.
Actually I didn't remove the cover plate due to safety concern, as much as I would like to do that. But I recommended in my report to have a certified electrician to take a look at the panel and breakers.
-
02-22-2012, 11:20 PM #13
Re: Old electrical Panels
I'd be into an article about that, too. Or even better for my purposes, a photo gallery of a bunch of panels with installation dates. I'm supposed to report when these things were installed, but don't know what to look for to date them. I've got a folder full of panel pics.
I've seen quite a few Stab-loks around here. I don't touch them; just seeing how uneven the switches look makes me not trust the things.
Ran across this last week. I pulled open a door next to a sink in a bathroom, and there it was.
Do not think of knocking out another person's brains because he differs in opinion from you. It would be as rational to knock yourself on the head because you differ from yourself ten years ago.
- James Burgh, 1754.
-
02-23-2012, 03:54 AM #14
-
02-23-2012, 04:56 AM #15
Re: Old electrical Panels
OOPs, sorry , thought you were in the lower 40.
Granted the system should more than likely be replaced, but
Did you run the toaster?
-
02-23-2012, 05:29 AM #16
Re: Old electrical Panels
Just terminology but I have always thought "split buss" was a panel that had a second set of buss bars to supply 120v breakers from one of the 240v breaker buss positions. This panel would look just like the diagram if the panel cover was off, one set of buss bars, one on the top half and one one the bottom. Only positions that can be 240 are right in the middle. Yes, no?
The beatings will continue until morale has improved. mgt.
-
02-23-2012, 07:34 AM #17
Re: Old electrical Panels
The buss layout in a split buss panel is "usually" like that in most panels where the spaces alternate which line they are tied to. Typically, the top of these panels have a two pole breakers for appliances like a range, dryer, AC, and whatever else may need 240 volts, and also has the breaker for the bottom buss. There can be up to 6 two pole breakers in the top so that the 6 disconnect rule is observed.
Many of these panels have a note on the label that limits the breakers in the disconnect (top) section to two pole breakers that gets ignored more times than not. It's not at all unusual to find 2 or 3 two pole breakers in this spot sharing the space with 6 single pole breakers
Two pole breakers work just fine in most of the "lighting" sections (bottom buss) but don't have the ability to power larger loads due to the limitation of the often installed 40 or 50 AMP breaker that powers it.
Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
-
02-23-2012, 10:40 AM #18
-
02-23-2012, 04:54 PM #19
Re: Old electrical Panels
I don't know why the photos did not load on my computer well enough to read them the other night, but tonight I can read that label (in the original post photo) fairly clearly and it is not a "split bus" panel as we are used to seeing, it is a "split phase" panel ("split phase" for lack of a better term where the phases are split to the top and the bottom) in that Phase A goes to the top bus and Phase B goes to the bottom bus. Only the center two breakers are capable of 240 volt circuits.
-
02-23-2012, 05:26 PM #20
Re: Old electrical Panels
It would be better, and easier to understand, if it was called what it is which is; single phase center tapped. It is all one phase with no voltage phase shift envloved. But we don't always call it what it is do we. (nice avitar
)
The beatings will continue until morale has improved. mgt.
-
02-23-2012, 05:45 PM #21
Re: Old electrical Panels
Except that it is not a "center tapped" panel.
Yep, it is not "split phase" either.It is all one phase with no voltage phase shift envloved.
But I could not think of a better term for it.
How about "single phase with in-line phase buses"? As compared to the modern "single phase with parallel phase buses" we all see every day.
Yep, if you ain't in one of them things on top(nice avitar)
, it ain't one of their panels on the bottom.
-
02-23-2012, 06:08 PM #22
Re: Old electrical Panels
Around here we would call that a form of split-bus panel. I haven't seen one of those in 20 years.
-
02-24-2012, 07:47 PM #23
Re: Old electrical Panels
Nope. Its mains lugs only (MLO) - on busses panel. (MLO) "Stab Lok".
It neither affords primary overcurrent protection for the panel, nor affords series protection for any sub-buss(es).
If you want to see what the "Guts" look like (with both 2-pole breaker positions filled with 1-P breakers) you can click here (clickable link):
http://inspectapedia.com/fpe/Federal...31-DJF-JSs.jpg
Federal Electric Products was the grand-daddy name of the company, The name was used for product produced both Newark, NJ for the US Market and Ontario, CAN, for the Canadian market. Newark's Federal Electric Products became FPE.
That is the old stab-lok breaker design, its just as problematic.
http://inspectapedia.com/fpe/Federal...32-DJF-JSs.jpg
AIC ratings (not "calculated" the same as now, and not tested as they are now either) insufficient for having no "upstream" series protection.
-
02-24-2012, 08:01 PM #24
Re: Old electrical Panels
Yes Vern, you are 100% correct.
This is an old (orignal style) stab lok panel. It is MLO, it affords no primary overload protection for the panel or any series protection for any self-contained sub-buss(es).
This panel has straight busses, they are one above the other, each has a mains lug upon it. You are correct as to where two 2-pole breakers are limited.
There are no sub-busses (which in a split-buss panel are series protected), it is not a "split buss" panel.
-
02-25-2012, 02:10 AM #25
Re: Old electrical Panels
Hi Eric
Never seen a good article on old panels and how to report them other than warnings here and there on brands such as Federal Pacific stabloc,or Zinsco.
Some think Pushmatic Bulldog need replacing also .
I report the three above and what I know but that is far as it goes.
Pushmatic I only recommend upgrade because it is hard to upgrade space wise and have been told some lenders demand it.
Maybe someone or you could do some research and write a good article on this subject .
-