07-14-2007, 01:24 PM #1
auto sensor location
...........
Similar Threads:Last edited by dan orourke; 01-01-2008 at 03:57 PM.
-
07-14-2007, 07:04 PM #2
Re: auto sensor location
While a bit further away than most I see, I think the critical dimension is how far the sensor is from the floor.
As long as the sensor reverses the door, and it's 5-6" from the floor, I'm OK with it.
JF
-
07-14-2007, 08:08 PM #3
Re: auto sensor location
It should be inline with the door IMHO....I would CMA and write it up.
-
07-14-2007, 08:17 PM #4
Re: auto sensor location
I have never seen a requirement to mount the sensor on the rail, and that looks like the supplied bracket. I would mention the hanging wire though.
-
07-14-2007, 08:57 PM #5
Re: auto sensor location
Height off the floor is the element being inspected. If sensor is on rail or not should not make any difference. I agree with Jim in that care should be taken to protect the wire ... or any wire so it does not become a trip hazard or accidental hook by something.
-
07-15-2007, 07:01 AM #6
Re: auto sensor location
I'm not sure what James meant by "It should be inline with the door IMHO", since it is obviously in line with the door.
I just pulled out the installation manual for my Genie opener. It is specific about the height. "Must be no more than 5" and less than 6" above the floor". It does not specify a side distance. It does say to install to inside door framing (not rail/track), but also says you can mount to the floor with brackets (not provided).
Since the opener will not work unless the sensors are installed in line with each other, I'm thinking that the side to side distance is not critical as long as they line up and operate correctly.
Of course the wires should be out of the way.
JF
-
07-15-2007, 08:15 AM #7
Re: auto sensor location
As it is ... it can't be in-line with the door. If it were, the railing would prevent the door from coming down.
I looks to be installed between the railing and the wall...
If that were the case, I would think this would not be right as a small child could actually be under partly of the door and not be between the rail and the wall.
RR
-
07-15-2007, 09:05 AM #8
Re: auto sensor location
Not only that, but if in line with the door, the door itself would cut the beam and reverse, you'd never be able to close the door.

-
07-15-2007, 10:08 AM #9
Re: auto sensor location
I should have said on the rail..sorry about that!
-
07-16-2007, 04:02 AM #10
Re: auto sensor location
Dan,
Did the sensors work and reverse the door?
Did they clear the door? (If they worked, I guess they cleared the door)
JF
By the way, they probably are set too high anyway.
-
02-21-2012, 10:00 AM #11
Re: auto sensor location
The auto sensors should be no less than 4" from the floor and no higher than 6" above the floor, correct? At least that's the criteria I've always used....now.....is that from code or manufacturer spec? I can't find it in the code.
Thanks,
Brian
-
02-21-2012, 11:44 AM #12
Re: auto sensor location
Go to the DASMA (Door & Access Systems Manufactureser Association) website and look at the Tech Data Sheets.
Specifically TDS #167, item #8, TDS #363, and TDS #364
http://www.dasma.com/PDF/Publication...ial/TDS167.pdf
"The Code is not a peak to reach but a foundation to build from."
-
02-21-2012, 03:11 PM #13
Re: auto sensor location
Thanks, Bruce.
What about the minimum height, according to the spec the sensors have no minimum height only a maximum height from the floor. Thoughs?
brian
-
02-21-2012, 08:23 PM #14
Re: auto sensor location
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.



Reply With Quote