Results 1 to 4 of 4
  1. #1
    Join Date
    May 2009
    Location
    New Jersey
    Posts
    90

    Default First time for this

    Today I found the refrigerator outlet on one of the small appliance counter circuits. 210.52 (b) (1) does not list refrigerators.

    Rich

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    georgia
    Posts
    112

    Default Re: First time for this

    I do not have the NEC section but it is close to this from the IRC and is pemitted.

    E3603.2 Kitchen and dining area receptacles.

    A minimum of two 20-ampere-rated branch circuits shall be provided to serve all wall and floor receptacle outlets located in the kitchen, pantry, breakfast area, dining area or similar area of a dwelling. The kitchen countertop receptacles shall be served by a minimum of two 20--ampere-rated branch circuits, either or both of which shall also be permitted to supply other receptacle outlets in the kitchen, pantry, breakfast and dining area including receptacle outlets for refrigeration appliances.

    Exception: The receptacle outlet for refrigeration appliances shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: First time for this

    Quote Originally Posted by paul hardy View Post
    Exception: The receptacle outlet for refrigeration appliances shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.
    The NEC is similar, note the key wording: The receptacle outlet for the refrigerator "shall be permitted to be" on a separate circuit.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: First time for this

    Not a problem according to the NEC.

    All answers based on unamended National Electrical codes.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •