    Default Heat duct in garage

    I am having a brain freeze here. What are some reasons why you would not want a heat duct from the furnace to exit into garage. It has no damper or grille, just a hole in the drywall, and a hole hacked i nto the metal duct. Thanks.

    Similar Threads:
    Inspection Referral
    Paul Kondzich
    Ft. Myers, FL.

  2. #2
    David Banks's Avatar
    David Banks Guest

    Default Re: Heat duct in garage

    R309.1.1 Duct penetration. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum No.26 gage sheet steel or other approved material and shall have no openings into the garage.

    Potential for gas vapors/carbon monoxide to be sucked into house.
    Break in firewall?


  3. #3
    Jon Randolph's Avatar
    Jon Randolph Guest

    Default Re: Heat duct in garage

    Don't forget about jeopardizing the fire wall by cutting through it.


  4. #4
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    187

    Default Re: Heat duct in garage

    Am I missing the phrasing of this? R309.1.1 Duct penetration. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum No.26 gage sheet steel or other approved material and shall have no openings into the garage.

    If it penetrates the space it must be no 26 or other approved metal. But it shouldn't penetrate the space.

    IMO, I prefer either a sleeve unit or if you can swing it, a ceiling hung unit...unless infrared is available. Ah hell, I should just live in FL.





  5. #5
    Jon Randolph's Avatar
    Jon Randolph Guest

    Default Re: Heat duct in garage

    Ross,

    I think that you are confusing penetrating and terminating.

    Penetrating (ie. going through) is the solid duct going through the space, which is allowed.

    Terminating, with an opening to the garage, could allow noxious fumes to enter the home and is not allowed.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Heat duct in garage

    Paul,

    Quote Originally Posted by Paul Kondzich View Post
    What are some reasons why you would not want a heat duct from the furnace to exit into garage.
    I believe this is confusing people, I know it is confusing me ...

    It has no damper or grille,

    just a hole in the drywall,

    and a hole hacked i nto the metal duct.
    Let's see if I have this right:

    No damper or grille ... but there is a hole in the duct supplying air to/taking air from the garage?

    26 gage can be run through (a "through penetration" when talking about a 'fire rated wall assembly', but a garage/living space *IS NOT* a 'fire rated wall assembly', it is only a 'separation wall') the garage wall, however, no return air is allowed to be taken from the garage or supply air given to the garage 'from the living space system' (there could always be a 'separate system' for the garage which only serves the garage).

    Another type of "penetration", but which does not apply here, is a "membrane penetration" (versus a "through penetration"). A "membrane penetration" is like an electrical box 'set into' the wall, it "penetrates" the membrane on one side of the wall, but it does not 'go through' the wall.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com