    I'm wondering about the wires attached directly to the main panel right side bus bar in this picture. I'm going to blame lack of sleep for me not picking this up when I was in there...
    There is sub panel in the detached garage - my guess is these are feeding it?

    Thanks!

    Jerry

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Jerry Harcek; 04-04-2012 at 09:19 AM. Reason: fixed picture rotation
    Member Benefits1

  2. #2
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Missing Breaker?

    It looks like the bottom right breaker feeds the garage panel.

    There is what looks like a range or drier circuit on 2 single breakers, # 3 & 4 from right top that should be on a 2 pole breaker.

    Looks like the arrangement of installed breakers has a total of 8 installed in the "service disconnects" part of the panel - 6 are permitted. Many of these panels restrict the breakers installed in the disconnect portion to 2 pole types so I'm guessing that's an issue here. The label would need to be checked.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  3. #3
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Missing Breaker?

    Both of these panels are a mess. The panel in photo #1 has neutrals attached to the EGC bus, possibly a violation of the six service disconnect rule, and multiple NM cables squeezed into one connector just for starters.


  4. #4
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Missing Breaker?

    Not to hijack the thread but the "6 service" disconnect as you call it is a debate I've had several times. I belive the code says "6 throws".

    Can you turn off more than one breaker on 1 throw? If you can turn off 4 breakers at one time, is that considered one throw? Sooooo possibly I can have 20 or so breakers and I am able to turn them all off within 6 throws, do I need a main disconnect?

    This may need to be a different post and I'm sure there is one somewhere on this forum.... Just food for thought!


  5. #5
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Missing Breaker?

    Here's what I see: An older house has had a service upgrade. There should be a main disconnect, as Bill pointed out, or no more than 6. Now that we have pics of the meter, it is clear that the larger panel is a main service panel and needs to be repaired.

    He neglected to install a tie bar on that range breaker feeding the cloth-covered wires, as Bill pointed out.

    The remote panel in the garage is the work of an amateur. Have an electrician install a cable clamp and repair the grounds with a proper terminal.

    There's plenty of repair work to do there.

    Last edited by John Kogel; 04-04-2012 at 09:30 AM. Reason: new info
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  6. #6
    Join Date
    Nov 2010
    Location
    Golden
    Posts
    16

    Default Re: Missing Breaker?

    I added a couple more pics and rotated the one of the main panel. Thanks for the help!


  7. #7
    Garry Blankenship's Avatar
    Garry Blankenship Guest

    Default Re: Missing Breaker?

    It would be nice to see that exterior service entrance panel w/o the dead-front cover to see the grounding, bonding and maybe where the bussing is split. It does look like the six disconnect rule is violated and any point beyond that panel the nuetral and ground wires should be isolated from each other.

    Sorry; I see one photo is the panel I thought was missing. Neutral wires on the ground buss ~ Already mentioned missing C/B handle increase the two many main disconnects and is a serious safety concern ~ Main service ground wire looks too small, but cannot be sure ~ Definitely non-professional work and that should be mentioned.

    Oh yea; peanut of half sized C/B are not allowed on the main section of a split buss panel.

    Last edited by Garry Blankenship; 04-04-2012 at 11:34 AM.

  8. #8
    Join Date
    Nov 2010
    Location
    Golden
    Posts
    16

    Default Re: Missing Breaker?

    Quote Originally Posted by Garry Blankenship View Post
    It would be nice to see that exterior service entrance panel w/o the dead-front cover to see the grounding, bonding and maybe where the bussing is split. It does look like the six disconnect rule is violated and any point beyond that panel the nuetral and ground wires should be isolated from each other.
    That's pic #2 of 4, I believe.


  9. #9
    Join Date
    Mar 2007
    Location
    Chicago
    Posts
    164

    Default Re: Missing Breaker?

    Quote Originally Posted by Wayne Carlisle View Post
    Not to hijack the thread but the "6 service" disconnect as you call it is a debate I've had several times. I belive the code says "6 throws".

    Can you turn off more than one breaker on 1 throw? If you can turn off 4 breakers at one time, is that considered one throw? Sooooo possibly I can have 20 or so breakers and I am able to turn them all off within 6 throws, do I need a main disconnect?

    This may need to be a different post and I'm sure there is one somewhere on this forum.... Just food for thought!
    Hi Wayne,

    The code does not say "6 throws". This, or any other variation is just jargon. (I personally have no problem with jargon depending on what it is and how it is used).

    The code says something to the effect of; no more than six switches and/or circuit breakers or a combination of switches and circuit breakers...... (something like that).

    No code book with me but it should be in Article 230 - Services, if anyone wants to check it out.

    Sincerely,

    Corey


  10. #10
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Re: Missing Breaker?

    E3601.7 Maximum number of disconnects. The service disconnecting means shall consist of not more than six switches or six circuit breakers mounted in a single enclosure or in a group of separate enclosures.

    James Bohac

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Missing Breaker?

    Quote Originally Posted by Wayne Carlisle View Post
    Not to hijack the thread but the "6 service" disconnect as you call it is a debate I've had several times. I belive the code says "6 throws".
    Nope, it is a maximum of 6 disconnects ... regardless of how many times one must attempt to "throw" the handle to off, or how many handles one can "throw" to off at the same time.

    - 230.71 Maximum Number of Disconnects.
    - - (A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be not more than six sets of disconnects per service grouped in any one location.
    - - For the purpose of this section, disconnecting means installed as part of listed equipment and used solely for the following shall not be considered a service disconnecting means:
    - - - (1) Power monitoring equipment
    - - - (2) Surge-protective device(s)
    - - - (3) Control circuit of the ground-fault protection system
    - - - (4) Power-operable service disconnecting means
    - - (B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with identified handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.
    - - - FPN: See 408.36, Exception No. 1 and Exception No. 3, for service equipment in certain panelboards, and see 430.95 for service equipment in motor control centers.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Missing Breaker?

    Okay.thanks all! Has the code recently changed? It's one of those dang moments when you think you remember what the code says and you go "oooops".

    Thanks for the comments and specific code sections.


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Missing Breaker?

    Quote Originally Posted by Wayne Carlisle View Post
    Okay.thanks all! Has the code recently changed?
    Nope.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Missing Breaker?

    The cover is NOT a "dead front", as the position knockouts have been removed exposing the buss and direct connection thereto when installed.

    Blanks or a new cover is necessary, in addition to relocating the minis, thins from the top half of the panel where they do not belong. I cannot make out the rating of the full-sized SP breaker on the lowest left top half buss. Service disconnects must be 75C not 60C.

    The panel diagram & labeling would identify what is and is not allowed and where, in the panel when used as service equipment, the date code for manufacture and Listing of the time period in relation to the UL marking guide for the product category as well as the associated edition of the UL White Book may prove helpful to you in addressing the concerns/questions raised.

    Last edited by H.G. Watson, Sr.; 04-06-2012 at 07:12 AM.

  15. #15
    Join Date
    Dec 2007
    Location
    Holladay, UT
    Posts
    577

    Default Re: Missing Breaker?

    I think Jerry H is referring to the wires you can see in the second picture. The right side breakers where there is a space it looks like there are wires attached directly to the bus bar. Is this what you are talking about Jerry H?

    Tom Rees / A Closer Look Home Inspection / Salt Lake City, Utah
    http://acloserlookslc.com/

  16. #16
    Scott Cook's Avatar
    Scott Cook Guest

    Default Re: Missing Breaker?

    The method of bonding the grounding conductors to the sub panel is both a violation and dangerous. NEC 408.40, 250.148(c), and 250.8(a). Yellow romex missing box connector, unlanded red wire not capped off, reduced size ground wire, neutral wire color cannot be remarked on 6 awg. and smaller.
    You could write a book on the problems with the service panel. It looks like they used the "spaghetti through a funnel"l method of Third World wiring.
    Suffice to say, it was not installed in a " neat and workman like manner". 110.12.

    No offense intended to the many Third World electricians whom actually do much better quality work than this.

    Last edited by Scott Cook; 04-06-2012 at 11:32 AM.

  17. #17
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Missing Breaker?

    I'm just soooooooo tired of DYI electrical A Physcian cannot treat him/her self. Why is it a Homeowner can burn/shock themselves?
    Oh ya, just remembered, So I can inspect it


  18. #18
    Robert Rolleston's Avatar
    Robert Rolleston Guest

    Default Re: Missing Breaker?

    What a mess that panel grounding is scary. And the main panel looks like the electrician forgot his wire cutters the last day so he just stripped the wires wadded them up and jammed the extra in there. And on the bottom he left a coil of white wire. I can see leaving some extra but the just looks like pure lazy here.