Results 1 to 12 of 12
  1. #1
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Metal pipe bonding

    Just checking, when PVC pipes are present do gas and any copper through separation wall still require bonding? I'm feeling like its a yes but wasn't sure.

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Metal pipe bonding

    Quote Originally Posted by Marc M View Post
    Just checking, when PVC pipes are present do gas and any copper through separation wall still require bonding? I'm feeling like its a yes but wasn't sure.
    I believe any metal plumbing pipe over 10 feet long needs bonding.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal pipe bonding

    Quote Originally Posted by John Kogel View Post
    I believe any metal plumbing pipe over 10 feet long needs bonding.
    Not as easy as that, at least not here in the states ...

    - 250.104 Bonding of Piping Systems and Exposed Structural Steel.
    - - (A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.
    - - - (not posting 1, 2, 3)


    - - (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

    Okay, define "system" ...

    In the places that I've been, the riser from the tub valve to the shower head, and the drop to the tub spout are *not* considered a "system".

    On the other hand, many builders used to run PB, and now PEX, underground as it can be installed as one continuous piece (no joints to leak), and, where that stubs up through the slab, they would switch to copper. All that copper was a "system" which needed to be bonded, each and every section of it which was discontinuous due to being connected to the plastic underground non-metallic piping.

    Is one 10 foot stick of copper a "system"? Probably not.

    Is a 50 foot long coil of soft copper run through the house a "system"? Probably.

    That is where the code is gray (there really are not many areas which are gray like that) and where the AHJ decides by interpretation.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Metal pipe bonding

    There are some that would not consider it a system unless it was the same material from start to finish. A partially metallic system would not meet their definition.

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal pipe bonding

    Quote Originally Posted by Jim Port View Post
    There are some that would not consider it a system unless it was the same material from start to finish. A partially metallic system would not meet their definition.
    Even if the underground was plastic by the entire rest of the house above ground was copper?

    The does *not* say "complete" system, just "system".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Metal pipe bonding

    In that example I would consider that a system even with the change in materials once the water enters the house.

    All answers based on unamended National Electrical codes.

  7. #7
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Metal pipe bonding

    So the reason I'm asking is out here there are a lot of homes re-piped in plastic but have copper in the garage up to the separation wall, then plastic. So its the garage pipes I'm mostly wondering about.
    Now that you're speaking about systems, I suppose the gas piping (a system) regardless of the interior supply piping still must be bonded...correct?


  8. #8
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Metal pipe bonding

    Quote Originally Posted by Marc M View Post
    So the reason I'm asking is out here there are a lot of homes re-piped in plastic but have copper in the garage up to the separation wall, then plastic. So its the garage pipes I'm mostly wondering about.
    Now that you're speaking about systems, I suppose the gas piping (a system) regardless of the interior supply piping still must be bonded...correct?
    The gas piping system is bonded through the EGC feeding a glass appliance, like the cord on a gas range. No further bonding is required. Newer systems with CSST piping may have further bonding requirements.


  9. #9
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Metal pipe bonding

    Quote Originally Posted by Robert Meier View Post
    The gas piping system is bonded through the EGC feeding a glass appliance, like the cord on a gas range. No further bonding is required. Newer systems with CSST piping may have further bonding requirements.
    So if the range is plugged in then there doesn't have to be a bond at the water heater for example, like in this pic?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  10. #10
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Metal pipe bonding

    Quote Originally Posted by Marc M View Post
    So if the range is plugged in then there doesn't have to be a bond at the water heater for example, like in this pic?
    IMO it's not required but may offer further protection as outlined in the FPN:

    250.104(B) Other Metal Piping. Where installed in or attached to
    a building or structure, a metal piping system(s), including
    gas piping, that is likely to become energized shall be
    bonded to the service equipment enclosure, the grounded
    conductor at the service, the grounding electrode conductor
    where of sufficient size, or the one or more grounding elec-
    trodes used. The bonding jumper(s) shall be sized in accor-
    dance with 250.122, using the rating of the circuit that is
    likely to energize the piping system(s). The equipment
    grounding conductor for the circuit that is likely to energize
    the piping shall be permitted to serve as the bonding means
    .
    The points of attachment of the bonding jumper(s) shall be
    accessible.
    FPN: Bonding all piping and metal air ducts within the
    premises will provide additional safety.



  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal pipe bonding

    Quote Originally Posted by Marc M View Post
    So if the range is plugged in then there doesn't have to be a bond at the water heater for example, like in this pic?
    If the gas piping is CSST, then it likely needs to have an additional bond to it.

    If the gas piping is steel piping, no problem, it is bonded through the grounding conductor.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Metal pipe bonding

    Schooled...thanks.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •