Results 1 to 4 of 4
-
05-21-2012, 05:46 PM #1
240v receptacle next to gas valve
240v receptacle for clothes dryer is very to gas valve. Both are recessed in a furred wall. Is it OK to have the electric and gas so close to each other? And the recessed installation is no good due to lack of access...correct?
Thanks.
Similar Threads:
-
05-21-2012, 06:54 PM #2
Re: 240v receptacle next to gas valve
They wind up close sometimes like another post of the stove outlet and the gas line. A larger access panel might be a good idea. But it looks like the dryer cord is fished in the wall. That would be a violation.
-
05-21-2012, 08:09 PM #3
Re: 240v receptacle next to gas valve
The photo is a bit dark but it looks like that is a box back in there with no cover, and if that is the case then the box needs to be brought forward to at least within 1/4" of the surface of the drywall and the drywall needs to be tight around the box - which would mean there would not be any access to the gas valve, so that means ... that it all needs to be corrected in some suitable manner as a 'quick and easy fix' will only create additional problems.
-
05-22-2012, 06:01 AM #4
Re: 240v receptacle next to gas valve
Looks to me like a surface mount receptacle has been enclosed in a wall. The receptacle either needs to be moved so it on the surface of the wall or replaced with a box and box mounted receptacle.
The dryer cord definitely can't be in the wall.
Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.



Reply With Quote
Bookmarks