Results 1 to 4 of 4
  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default Electric furnace disconnect switch

    Last edited by Jeff Eastman; 12-11-2007 at 07:06 PM.
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Electric furnace disconnect switch

    Yes. The disconnect should be in the closet with the furnace.

    I know, someone is going to say 'but you are not going to be 'in' the closet and close the door, so you can still see if someone comes by and flips the breaker back on', yes, that is true, but ...

    The disconnect still "should be" in the closet, and that was the question.

    What is that stubbed out of the wall below the panel? A water cooler?

    This is that commercial building right (I can see the drop ceiling lay in tiles)? Definitely in that case.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3

    Default Re: Electric furnace disconnect switch

    The disconnect still "should be" in the closet, and that was the question.
    If a disconnect is required in that closet, couldn't you just place a lock out on the breaker in the panel as an alternative?


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Electric furnace disconnect switch

    Quote Originally Posted by Brandon Whitmore View Post
    If a disconnect is required in that closet, couldn't you just place a lock out on the breaker in the panel as an alternative?
    Not if that is "air conditioning or refrigeration" equipment.

    If it was *only* a "furnace" (heat only), maybe, I'd have to look that up, but not if there is also "air conditioning" equipment there too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •