Found this S-trap repair at inspection today. There is a trap behind leg of pedestal sink (couldn't get good picture of). They installed mechanical vent at top of pipe where it goes up under sink in first picture. Will this stop water from siphoning out of trap? What do you think?
Similar Threads:
-
06-30-2012, 04:12 PM #2
Re: S-Trap
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
06-30-2012, 04:13 PM #3
Re: S-Trap
Billy, There is a trap behind the pedestal where chrome pipe starts, you just can't see it.
-
06-30-2012, 04:16 PM #4
-
07-01-2012, 07:06 AM #5
Re: S-Trap
No S-trap present. My guess is there used to be an S trap set-up, they got dinged for it and the repair with the mechanical vent was their way of fixing it.
-
07-01-2012, 07:27 PM #6
Re: S-Trap
Markus, In your opinion is this a good fix? I also use that line a lot. The code is a minimum requirement.
-
07-01-2012, 09:12 PM #7
Re: S-Trap
I don't know what Markus thinks of it, but it is acceptable to me. The chrome trap will not siphon with the AAV in the line. In some jurisdictions they don't allow an AAV.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
07-02-2012, 04:51 AM #8
Re: S-Trap
It is fine. Minimum 4" up from trap.
-
07-02-2012, 05:37 AM #9
Re: S-Trap
As a fix it's fine for me if that type of arrangement is allowed in that area. Most of the time if an old S trap has been DIY replaced they just put in a 90 on top of the pipe going into the floor, trap at the fixture and no venting at all.
That AAV set-up however isn't allowed around here; so i would have to write it as non-compliant.
i was in paris and saw an AAV on a toilet run, so whether an AAV fine or not i guess really depends on perspective.
Yeah, developers really hate it when you explain to the client that the Code is a minimum standard. Especially rough when they've spent so much time telling the client they build to Code.
Last edited by Markus Keller; 07-02-2012 at 05:44 AM. Reason: add pic
-
07-02-2012, 05:42 AM #10
-
07-02-2012, 06:01 AM #11
-
07-02-2012, 06:50 AM #12
Re: S-Trap
Markus, Love your vacation picture.
-
07-02-2012, 04:46 PM #13
Re: S-Trap
I feel like I am quoting the entire thread here, but it is really only just a few posts:
Firsts, the drawing Rich posted is an incorrect drawing. The drawing shows 4" between the AAV vent and the top of the fixture arm, which is incorrect, the 4" is measured between the AAV vent and the trap weir, which is the top of the bottom of the fixture arm at the trap end - see modified drawing.
Billy, yes, if an AAV is PROPERLY installed on an S-trap, then it is no longer an S-trap, it is a properly vented trap. Which would make it an approved fix.
Not that the first reference in this thread to that AAV was to it as a "mechanical" vent, and an AAV is not a mechanical vent, it is an air admittance valve.
-
07-02-2012, 05:10 PM #14
Re: S-Trap
Regards to Jerry saying my diagaram is incorrect......
This diagaram, shows the same 4", measured the same way.
The digaram is from the "Code Check Series" of books. / illustrations.
I dont know, maybe the so called "experts" are all wrong.
One says on thing, one says another.
"Code Check" is considered a fairly good resorce for inspectors!
But thanks Jerry
-
07-02-2012, 05:40 PM #15
Re: S-Trap
Unfortunately, those references are also incorrect at times, just like I am, only this time I am not the one who is incorrect:
Over the years we have, on this site, found many errors in the Code Check references - while the Code Check references are an excellent reference guide, they are not code or installation instructions.
As you said: ""Code Check" is considered a fairly good resorce for inspectors!", and you should take it as just that.I', not knocking them, just agreeing with you.
This: "The air admittance valve must be located a minimum of 4 inches above the weir of the trap. However, the valve may be located below the flood level rim of the fixture being vented." is from page 5 here: http://www.studor.com/DesignCriteria.pdf
That is from the horse's mouth, so to speak ... that IS the correct information, and is what I said.
-
07-02-2012, 05:44 PM #16
Re: S-Trap
[QUOTE=Kevin Wood;201986]IRC 2006 P3114.4 Location. Individual and branch air admittance valves shall be located a minimum of 4 inches above the horizontal branch drain being vented.
This would tell me that it is not from the weir but from the crown.[/qutoe]
I realize you had not read my post above as I was typing as you were posting.
And the picture we started with cannot be corrected by just an AAV.
Please explain to me why the AAV did not, and cannot be used to, correct that.
-
07-02-2012, 05:48 PM #17
Re: S-Trap
Jerry,
Looks like just another opinion to me. No Code referances.
I'm not knocking you at all, You have helped me many times,
but some people get a bit carried away here. Measured from the
top / the bottom! Its a drain, not brain surgery!
A published book on "codes", is good enough for me.
Thanks Again
-
07-02-2012, 06:00 PM #18
Re: S-Trap
Thank for the code ref Kevin.
The "code diagaram" I posted appears proper.
-
07-02-2012, 06:01 PM #19
Re: S-Trap
Rich,
"Looks like just another opinion to me."????
That is from the MANUFACTURER and that is HOW it is REQUIRED to be INSTALLED.
As you wish, just don't hang your hat on those other references which are just opinions. It's your neck and your reputation, not mine. Go for it.
-
07-02-2012, 06:03 PM #20
Re: S-Trap
-
07-02-2012, 06:03 PM #21
Re: S-Trap
Again.... IT's a drain! and were talking about minor measurment issues
that will not make much of a differance.
But thanks
-
07-02-2012, 06:07 PM #22
-
07-02-2012, 06:20 PM #23
Re: S-Trap
"minor measurment issues that will not make much of a differance"
Apparently there is some knowledge missing on just how critical those measurement issues are and just how much difference they will make.
Do you know why there is a limit to the length of a trap arm and why that length is based on the size of the pipe in the trap arm?
Yeah ... "IT's a drain!" ... and you want to keep draining, don't you!
I ask again, you, Kevin, Billy, or anyone:
Originally Posted by Jerry Peck
-
07-02-2012, 07:20 PM #24
Re: S-Trap
Okay, we agree there, at least the two of us do.
As for the 4 inch rule it should be at the top crown anyways as this is better than being lower.
Code and installation instructions address things in a way which allows/prohibits things, such as 'at least'/'not less than'/etc (minimum) or 'shall not exceed'/'maximum'/etc (maximum).
One example of a stated maximum is:
- TABLE P3105.1
- - MAXIMUM DISTANCE OF FIXTURE TRAP FROM VENT
The reason for the above is this:
- P3105.1 Distance of trap from vent. Each fixture trap shall have a protecting vent located so that the slope and the developed length in the fixture drain from the trap weir to the vent fitting are within the requirements set forth in Table P3105.1.
- - Exception: The developed length of the fixture drain from the trap weir to the vent fitting for self-siphoning fixtures, such as water closets, shall not be limited.
It is the trap weir which rules with regard to distances, and the maximum length of the fixture drain must not exceed a length which will cut the air off at the vent fitting, which does not mean "at the vent fitting" per se, but at the top of the inside of the vent fitting. I.e., you can take a length of pipe and look through the opening at one end with the pipe level, now lower the other end of the pipe, when you can no longer see daylight through the opening at the other end, that slope, for that size pipe and that length of pipe, will no longer vent. See attached drawing.
I don't like to mention code and I certainly would not put it like the manufacture says unless this was standard practice taught by Carson Dunlop, InterNachi, IRC and any others that I have gone through.
I do believe they made a mistake on the PDF it happens all the time.
-
07-02-2012, 08:13 PM #25
Re: S-Trap
Phoenix AZ Resale Home, Mobile Home, New Home Warranty Inspections. ASHI Certified Inspector #206929 Arizona Certified Inspector # 38440
www.inspectaz.com
-
07-02-2012, 08:36 PM #26
Re: S-Trap
Fla. Jerry has got his 'trap' weir and his 'crown' weir mixed up again. The diagram R.S. posted was exactly correct.The Studor min. is 4" (+ depending on trade size of the plumbing employed)above the CROWN weir - that's top (air/pressure) side escape, not trap spill (liquids/solids) point (trap weir).The compartmented or 'partition' "trap" was NOT pictured, as per the OP, it is chromed and is set in the ped. before the trap arm. There is no "vented 'S' " trap, period (.) exclamation point (!).
The section he quoted most recently above has NOTHING to do with the required height ABOVE the crown weir, but refers to the DEVELOPED LENGTH beyond the trap weir for a trap arm BEFORE the vent. He's talking apples and oranges, and although BOTH factors must be considered in the fluid dynamics, scour, maintaining trap seal, etc. they are distinctly and completely DIFFERENT prescriptions and proscriptions.
Technically, the diaphram IS a moving part, hence the 'mechical' nature of the air admittnce VALVE, (which does not VENT, as in 'plumbing' DWV), but admits air only, WHEN it is functioning properly. The A.A.V. is an ALTERNATIVE to venting which is approved in limited jurisdictions with LIMITATIONS. It is a substitue for fixture venting but does not actually vent (exit, escape) directly (think of it as the 'Roach Motel' or 'Hotel California' of venting alternatives - when working properly, it lets air IN so as to displace/equalize/allow (prevent vacuum) for the drainage/waste to flow but doesn't let air/vapors EXIT/VENT directly via the device -- to ATMOSPHERE).
Last edited by H.G. Watson, Sr.; 07-02-2012 at 09:22 PM.
-
07-03-2012, 05:46 AM #27
Re: S-Trap
I want to make sure I understand this. It is the horizontal run that makes this not a S-trap? I'm talking about my original picture.
Last edited by Tom Rees; 07-03-2012 at 06:02 AM.
-
07-03-2012, 06:07 AM #28
Re: S-Trap
Thanks Kevin
-
07-03-2012, 06:38 PM #29
Re: S-Trap
You have yet to post where the code is more stringent. The previously posted code language does not specify where the measurement is too - unless I missed it, if so, please point it out. Thanks.
My Studor vent pdf says above the crown by 4".
-
07-03-2012, 06:43 PM #30
Re: S-Trap
-
07-03-2012, 06:49 PM #31
Re: S-Trap
-
07-03-2012, 08:12 PM #32
-
07-04-2012, 03:18 AM #33
Re: S-Trap
studor isn't the only rodeo in town
other mfr instruct 4" min. above horizontal branch/trap arm
hard to understand a diagram being wrong if the weir ht. plus pipe dimension exceeds 4" minimum
http://quickvent.net/images/quickven...ction_i917.jpg
http://www.oatey.com/apps/catalog/in...ctionSheet.pdf
y'all have a great 4th and try not to stress over those diagrams
Last edited by BARRY ADAIR; 07-04-2012 at 03:27 AM.
badair http://www.adairinspection.com Garland, TX 75042
Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
life is the random lottery of events followed by numerous narrow escapes...accept the good
-
07-04-2012, 05:50 AM #34
Re: S-Trap
From Barry's PDF the installation instructions qoute the trap be 6 inches above flood rim level, I have seen this before. This would be impossible in most applications I have seen because the vent is under cabinet? Could somebody clarify please, Thanks. Oops, read again and that is one of the options, where the hell would a recessed box be.
-
07-04-2012, 09:39 AM #35
Re: S-Trap
Tom Rees,
Regarding your OP and the following wandering converstation:
This does not appear to be a vent stack or stack vent alternative - but an individual (fixture) or branch vent alternative, with AAV and doesn't appear to be a compliant installation as you have BOTH described AND pictured.
The Plumbing chapters of the IRC (IF adopted, and IF adopted unmmended) and the applicable sections & subsections of the IPC (IF adopted, and IF adopted unmmended), provide for a permissive use of an AAV IF employed as per "the code", period.
Both the IPC and the IRC plumbing chapters require the trap, trap arm, drainage, and/or stack meet the STRICTER requirements of "the code" (prescriptions and proscriptions) FIRST, AND additionally the manufacturer's instructions. The "Code" requires a greater minimum height than Jerry Peck's "opinion" of an un-referenced, supposed, manufacturer's instruction - which I disagree as to his uneducated "opinion", as to just WHAT that supposed unadulterated language is referring to, "engineering", etc.-wise, anyway. The use is limited as to its APPROVAL - and again - limited to the restrictions of THE CODE.
Originally Posted by 2009 IRC
Originally Posted by 2009 IRC
Originally Posted by 2009 IRC
Originally Posted by 2009 IRC
Originally Posted by 2009 IRC
Originally Posted by 2009 IRC
Others have represented that their INCORRECT application of language from certain unreferenced documents in some way SUPERCEED the RESTRICTIVE (proscriptive) and required language (prescriptive requirements) and PERMISSIVE, but CONDITIONAL (allowances, alternatives which are not required but IF employed MUST meet requirements of "the code") of both the IRC (multiple editions) and the IPC.
There is no validity in J. Peck's assertion that his misintrepretation of manufacturer's language regarding minimum height above a horizontal trap arm in anyway superceeds the MINIMUM height requirements of the IRC or IPC. Both 'codes' REQUIRE a MINIMUM height above the TOP of the horizontal arm or branch for the AAV (four inches). A misprint or misreading indicating LESS than that four inches WOULD NOt be compliant WITH EITHER THE IPC OR IRC.
The original "code check" diagram posted by another, IS EXACTLY CORRECT. Jerry Peck's "modification" and assertions regarding same is WRONG.
The minimum developed length between the trap weir and any vent or vent alternative - is a COMPLETELY different topic.
Most of the continuing discussion has been muddled and wrong.
The pictured and described is NOT an "S" Trap. Those metal partition traps sold with fixtures are just that.
The pictured and described fixture drainage & venting plus AAV installation requires correction to meet IPC or IRC applicable chapters, sections & subsections IF adopted unammended in your jurisdiction - at the time the work was done.
It would not have met UPC requirements prior.
Regarding your most recent post immediately above, and quoted below:
Originally Posted by Tom Rees
(2.) An individual or branch type AAV is the type which is employed venting off a HORIZONTAL drain, trap arm, branch, etc. These are the type which must be a minimum of FOUR inches ABOVE the horizontal (lateral) DRAIN (pipe) and can be found when properly installed under a lavatory or sink in a cabinet.
Two different "type" AAVs - two different requirements - one is employed off (above) a horizontal drainage pipe - the other is installed atop a stack pipe (vertical).
Traps ABOVE flood level rims wouldn't make sense for gravity drainage of lavatory. Pumps are a different matter - and AAVs, etc. aren't allowed non-engineered situations.
(3.) For in-the wall, floor/ceiling, etc. plumbing - a recessed "box", generally with an accessible & removable grille cover allowing for air-flow/venting and to disquise the plain view, or without a cover if employed in-the-wall behind an open lavatory/sink cabinet; are often found in-the-wall recessed from the wall covering, or in-the-ceiling (floor/ceiling cavity).
HTH.
Last edited by H.G. Watson, Sr.; 07-04-2012 at 10:38 AM.
-
07-04-2012, 10:36 AM #36
Re: S-Trap
I keep pointing this out, but I guess I have to post it too - the IRC *does not state what some are saying it does*:
- SECTION P3114
- - AIR ADMITTANCE VALVES
- - - P3114.4 Location. Individual and branch air admittance valves shall be located a minimum of 4 inches (102 mm) above the horizontal branch drain or fixture drain being vented. Stack-type air admittance valves shall be located a minimum of 6 inches (152 mm) above the flood level rim of the highest fixture being vented. The air admittance valve shall be located within the maximum developed length permitted for the vent. The air admittance valve shall be installed a minimum of 6 inches (152 mm) above insulation materials where installed in attics.
That does *not* state that you measure from the top as some of you guys are saying. The manufacturer, on the other hand, does state where to measure from.
-
07-04-2012, 10:49 AM #37
Re: S-Trap
It actually DOES SAY that Peck. I already quoted the sections & subsections that apply.
Obviously you don't KNOW (or have forgotten yet again, or confused yourself, YET AGAIN) as to what the words, terms, and phrases especially regarding prescriptives and permissives, orientation, etc. being used in "the code" (IRC plumbing chapters, IPC) actually MEAN as petains to plumbing, drainage, venting, the standards incorporated & referenced therein, etc.
Even a "plain languge" reading of the section you re-quote clearly states this.
P3114.4 Location. Individual and branch air admittance valves shall be located a minimum of 4 inches (102 mm) above the horizontal branch drain or fixture drain being vented. Stack-type air admittance valves shall be located a minimum of 6 inches (152 mm) above the flood level rim of the highest fixture being vented. The air admittance valve shall be located within the maximum developed length permitted for the vent. The air admittance valve shall be installed a minimum of 6 inches (152 mm) above insulation materials where installed in attics.
Just what do you THINK constitutes a "horizontal drain"???
Last edited by H.G. Watson, Sr.; 07-04-2012 at 11:03 AM.
-
07-04-2012, 11:45 AM #38
Re: S-Trap
It actually DOES NOT SAY THAT, WATSON. YOU ARE ADDING YOUR IMAGINATION INTO IT AGAIN.
Originally Posted by Jerry Peck
The code states that you measure 4", yep - it does, the code does not state that you measure it from the top of the pipe, nope - it does not.
Just what do you THINK constitutes a "horizontal drain"???... where was "the top" you would measure from? Oh, wait, you measured above the trap weir ... yeah, those open drains are no longer allowed.
It does not matter if you are using 1-1/4" for a lavatory or 6" for a lavatory, the trap weir *will be the same* ... *the height of the pipe will change*.
Last edited by Jerry Peck; 07-04-2012 at 01:07 PM. Reason: fixing a quote - missing "]" at end
-
07-04-2012, 02:36 PM #39
Re: S-Trap
You're beyond reason Peck!
As usual you resort to personal attacks, name-calling and non-professional behavior in yet-another-of your "classic" tantrums, when you stick your virtual foot in your virtual mouth on a subject you do not understand.
You do NOT measure the elevation for a vent from the trap weir! You measure the developed length of the arm (prior to vent opening) from same.
A dry vent opening for a horizontal drain may not begin/connect below the center-line (half-point) of a horizontal drain pipe.
P3104.3 Vent connection to drainage system. Every dry vent connecting to a horizontal drain shall connect above the centerline of the horizontal drain pipe.
I suspect you have lost your marbles and/or desperately burring your blunders and lack of understanding of fluid dynamics, in B.S.
Last edited by H.G. Watson, Sr.; 07-04-2012 at 02:42 PM.
-
07-04-2012, 03:08 PM #40
Re: S-Trap
Not to worry, Watson, you've been so far beyond reason and reasonable for so long that we ignore as much as possible.
As usual you resort to personal attacks, name-calling and non-professional behavior in yet-another-of your "classic" tantrums, when you stick your virtual foot in your virtual mouth on a subject you do not understand.
You do NOT measure the elevation for a vent from the trap weir! You measure the developed length of the arm (prior to vent opening) from same.
... Oh, wait! I just got it! Man you are good! You ALMOST got me on that one! That was just another one of your re-direction shuffle attempts to mis-direct us from your incorrect answers to another answer for a question which was not asked ... I ALMOST missed that effort on your part ... ALMOST missed it, but I got it as I was typing my reply.
Sheesh, Watson, you ALMOST had me on that mis-direction re-direction shuffle - sorry to say, Ol' Buddy, but you suffered a loss of yardage on that play.
-
07-04-2012, 03:42 PM #41
-
07-04-2012, 03:55 PM #42
Re: S-Trap
.
Alright Lets leave Him outta this.
.
Stupenous man image by elvisdaking on Photobucket
.
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
07-04-2012, 04:18 PM #43
Re: S-Trap
oops, dropped a 'D'.