Has anybody found this problem 5 ton compressor and four ton coil.
That doesn't work. and after replacing the coil to a five ton did it solve the problem?
Similar Threads:
-
08-07-2012, 07:09 AM #2
Re: Miss match compessor & coil
-
08-07-2012, 07:14 AM #3
Re: Miss match compessor & coil
It can be done, perhaps sometimes successfully. Ask your dealer for the AHRI reference number, certificate of match.
Last edited by Aaron Miller; 08-07-2012 at 07:16 AM. Reason: Typo
Texas Inspector
http://www.texasinspector.com
What the plainspoken man lacks in subtlety, he makes up in clarity.
-
08-07-2012, 09:42 AM #4
Re: Miss match compessor & coil
The house I purchased for myself this last year has a 2.5 ton compressor and the evaporator is only 2 ton. I inspected the home and reported the AC worked correctly. temp slit was 20 degrees. I never crossed referenced the two and had no idea. After moving in I found that when the AC is operated for several hours, The evaporator completely ices up and no longer works. My wife says we should sue the home inspector

-
08-07-2012, 07:58 PM #5
-
08-07-2012, 09:11 PM #6
Re: Miss match compessor & coil
-
08-07-2012, 11:46 PM #7
Re: Miss match compessor & coil
What is a TXV valve? Is that an expensive part and exactly what would that do to prevent the icing on the evaporator?
-
08-08-2012, 01:46 AM #8
Re: Miss match compessor & coil
No We are replacing coil with five ton do yoy think this will this solve the problem? Bob did you replace coil and did it fix the problem?
-
08-08-2012, 03:47 AM #9
Re: Miss match compessor & coil
A TXV "Thermal Expansion Valve" is an active metering device used in place of a fixed orifice metering device. The TXV measures the temperature of the end of the evaporator coil and adjust the amount of refrigerant metered into the coil. They are not that expensive to buy, somewhere around $100. Putting them in is not all that hard but will add to cost depending on what kind of friends you have.
The beatings will continue until morale has improved. mgt.
-
08-08-2012, 04:28 AM #10
Re: Miss match compessor & coil
Art,
There are several questions you must have answered before you can arrive at an answer to resolving the equipment miss mach.
If you just install a matched coil you system it may not work.
1) Was the comp/coil sized to your house by a Manual J ?
2) What system size were your ducts sized for ?
3) Was your system designed for an AC split system or a Heat Pump ?
4) Is your air handler capable to handle the air flow requirements of the system?
There are more but that is a basic start to begin to determine what can or can not be done.
Your question is more complicated than you may want to believe.
Bring in a competent HVAC person and have him evaluate your entire system including the ducts and also do the Heat Loss Analysis (Manual-J).
The underlying question may be why was the 5 T comp installed?
Also, if the installer made a mistake in the equipment, what else did they do wrong ?