Results 1 to 5 of 5
  1. #1
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,153

    Default is this a zinsco -sylvania breaker-panel

    hey guys

    came across this today and first time i have seen the red and blue breakers that were not the sylvania brand--these breakers said MURRAY--is that still a product of the bad guys--also found difFerent brand breakers in paneL--is this allowed

    DOING REPORT NOW

    THANKS

    CVF

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Gerry Bennett's Avatar
    Gerry Bennett Guest

    Default Re: is this a zinsco -sylvania breaker-panel

    I don't think I ever saw a zinsco slyvania, but I have seen plenty of Murray panels. You can still get Murray breakers, even in Depot. They are not color coded any more. Blue was 15amp, red 20, green 30, and I think grey was 40. Don't know after that. As to the other brands in there they are probably not listed for that panel.


  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: is this a zinsco -sylvania breaker-panel

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    hey guys

    came across this today and first time i have seen the red and blue breakers that were not the sylvania brand--these breakers said MURRAY--is that still a product of the bad guys--also found difFerent brand breakers in paneL--is this allowed

    DOING REPORT NOW

    THANKS

    CVF
    No, they are not the same.. Sylvania-Zinsco throw handles are in the opposite direction so it makes it almost impossible to remove the dead font without turning te breakers off.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Jeffrey Maul's Avatar
    Jeffrey Maul Guest

    Default Re: is this a zinsco -sylvania breaker-panel

    There's nothing wrong with Murray breakers but I's be concerned with the total number of half-size/double breakers in this particular panel and whether this panel is designed to accept double breakers. The bus in some panels will not accept double breakers which need a notch in the buss. Some not-so reputable installers will break the slot in breaker to opened it up (with pliers). I'd remove one and see if anyone tampered with it.
    If not there still may be a limit to the number of double breakers specified by the manufacturer.


  5. #5
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: is this a zinsco -sylvania breaker-panel

    No to the title question, and Yes other brands are allowed.

    Label, marking, or information & diagram in pocket:

    For example (FYI "W" in circle stands for Westinghouse, and Murray is now Siemens IIRC, successor companies also for some other brands mentioned in following) Main issue to verify ratings for svc. equip panel are met by replacement breakers installed within, and that the EPs are only installed where the panel diagram indicates they are permitted; and the old 10 amp rule per pole on bus stab by vintage of ol' listing standard rules regardless of load calcs).:



    Last edited by H.G. Watson, Sr.; 09-21-2012 at 07:49 PM.