Results 1 to 9 of 9
			
		- 
	10-11-2007, 11:51 AM #1 Different sized furnace vent pipe segments Different sized furnace vent pipe segments......... 
 Similar Threads:Last edited by Clay White; 01-02-2008 at 04:09 PM. 
 
- 
	10-11-2007, 12:33 PM #2 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsClay, 
 
 The size of the SW Vent doesn't bother me the distance to combustibles does.
 
 Also I can't see any screws to connect B1 to SW Vent.
 
 Appears be water stained by SW Vent patched? Active Leak?
 It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
 Billy J. Stephens HI Service Memphis TN.
 
- 
	10-11-2007, 02:53 PM #3 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsLooks like a single wall vent going through the ceiling. I would be concerned about clearance to combustibles. 
 
 
- 
	10-11-2007, 03:35 PM #4
 
- 
	10-11-2007, 05:18 PM #5 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsSorry, 
 
 I looked at the pic and read the original post but I guess that I didn't see your comment.
 
 We need an icon to designate "foot in mouth"
 
 
- 
	10-12-2007, 07:04 AM #6 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsThe section that runs into the ceiling is a B-vent. In our area of N. Illinois condensation formation is a very frequent occurrence and I suspect that this installation would lead to problems if installed here. 
 
 I think that it's warranted to question this installation. The problem is that the contractor may have no understanding of your reasoning is.
 Eric Barker, ACI
 Lake Barrington, IL
 
- 
	10-12-2007, 07:12 AM #7
 
- 
	10-12-2007, 08:49 AM #8 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsHey Clay, I agree with Eric on the b vent through ceiling. I do not see any connection between the vent increaser and the existing vent. I looks like tabs on b vent so there should be a snap ring. Screws would be ok provided they don't penetrate the inner wall of the vent. Also would also need 1" clearance around. By the way does the furnace have a draft inducer motor? 
 
 
- 
	10-12-2007, 07:14 PM #9 Re: Different sized furnace vent pipe segments Re: Different sized furnace vent pipe segmentsYes it is a problem; the vent system is designed to flow at the size of the outlet of the combustion chamber. And yes condensation will likely form and run back down to the combustion chamber. I also am a HVAC contractor and this type of set up has made me money before. 
 
 


 
 
						
					
 
				
				
				
					 Reply With Quote
  Reply With Quote 
					
					 Originally Posted by Billy Stephens
 Originally Posted by Billy Stephens
					


Bookmarks