Thread: Separate circuit for gas dryer?
11-12-2012, 03:27 PM #1
I had a question while reading through this thread http://www.inspectionnews.net/home_i...-required.html and decided to start a new thread since this is an electrical question.
If you convert to gas can you share the washing machine circuit for the dryer?
Is there an acceptable way to convert the 240 circuit to 120? Junction box?
11-12-2012, 03:46 PM #2
Re: Separate circuit for gas dryer?
The dryer should be able to share the washer circuit.
I would leave the 240 dryer receptacle alone.
11-12-2012, 03:53 PM #3
Remove the 240v breaker, replace with a 20amp 120v breaker
Connect 1 wire of the electric cable to the breaker
Connect the other wire to the neutral bus
Leave the groung wire connected to the ground bus
Replace the 240v dryer receptacle outlet with a 120 receptacle outlet
Hot wire to the hot terminal (brass screws)
Netural wire to the neutral terminal (white screws)
and connect the ground wire to the ground terminal (green)
Turn on breaker, test for outlet for proper voltage and polarity
Install outlet cover
Install blank cover in missing panel box cover.
Replace panel box cover
Don
You now a have 120v outlet fro the dryer where there was a 240v outlet
11-12-2012, 07:24 PM #4
11-12-2012, 07:32 PM #5
11-12-2012, 09:02 PM #6
You should not mess with the dryer circuit for a number of reasons, #1 being the 120 volt duplex receptacle isn't designed for a conductor that size, #10.
Number 2, the confusion of translating the instructions could lead to a shock hazard.
Number 3, someone could decide to shortcut the process by leaving the breaker as is in the panel, shock and fire hazard.
Number 4, the dryer receptacle should be left there for future use. There are washing machine which heat water and run on 240 volts. New appliances are coming out all the time.
11-13-2012, 07:24 AM #7