What is the switch on the transformer for?
Note the pulleys used to turn on and off the transformer from the ground.
Is this an service disconnect?
Thank you.
Similar Threads:
-
11-21-2012, 05:22 PM #2
Re: Pole Transformer
Yes, it is a service switch for the pot.
I have NEVER seen a rig like that to actuate the switch. Looks home-made to me.
-
11-21-2012, 06:14 PM #3
Re: Pole Transformer
-
11-21-2012, 06:29 PM #4
Re: Pole Transformer
Thanks gentleman.
Another question if you please...
200 amp service, note the solid multiple wires between the two lugs.
What am I seeing?
Thank you.
-
11-21-2012, 07:18 PM #5
Re: Pole Transformer
Yes here it is.
-
11-21-2012, 07:37 PM #6
Re: Pole Transformer
-
11-21-2012, 08:05 PM #7
Re: Pole Transformer
Hi Jerry I understand 3 phase but " fire starter" Does that prevent voltage drop on the start leg? I don't get it.
-
11-21-2012, 08:27 PM #8
Re: Pole Transformer
The third insulated line in the middle lug went out to the pole but was not attached to the transformer. Only two wires from the transformer and the bare neutral guide wire.
-
11-21-2012, 08:27 PM #9
Re: Pole Transformer
I get it now. Cheaper than replacing a 3 phase breaker or disconect with a bad leg
-
11-21-2012, 08:30 PM #10
Re: Pole Transformer
Is this something that should be repaired by electrician? Is it safe as is?
-
11-21-2012, 08:41 PM #11
Re: Pole Transformer
If it was me have it repaired. The way i see it is three legs ,one out, one of the other legs has to carry the load for the down leg. High amperage draw on one leg and high heat. That's just me. If it don't look right,it probally isn't.
-
11-21-2012, 08:55 PM #12
-
11-21-2012, 08:57 PM #13
Re: Pole Transformer
10-4 thanks!
Will inform client to have an electrician investigate further.
Much obliged.
-
11-21-2012, 09:11 PM #14
-
11-22-2012, 05:55 AM #15
Re: Pole Transformer
Fwiw.
Short of the misfiring, misuse of this panel FPE are not the same as state side and have never been recalled in Canada, except for a number of years ago when they had a recall on breakers.
-
11-22-2012, 07:57 AM #16
-
11-22-2012, 09:23 AM #17
Re: Pole Transformer
The issues are improper use of multiple small gauge wires for a jumper.
Lugs not designed for multiple conductors.
Dead conductor should be removed for safety.
The center bus is hot, but one of the outers is dead, disconnected at the pole, and was jumped (by an amateur pyromaniac).
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
11-22-2012, 09:58 AM #18
Re: Pole Transformer
Thanks John, that does make sense.
I have informed my clients to seek further assessment from an electrician.
-
11-22-2012, 10:48 AM #19
Re: Pole Transformer
Referring it out was definitely the right thing to do. Like others that rope or cable actuated pole xmfr disconnect is totally foreign to me. I sure hope is was rope and not conductive cable. The panel looks to be three phase supplied by single phase and the owner jumped two of the legs together to get more circuit breaker mounting space. The jumpers are illegal for multiple reasons. That pole has seen better days.
-
11-22-2012, 02:11 PM #20
Re: Pole Transformer
Hi Garry,
Yes they were ropes to the pulley.
Thanks,
-
11-22-2012, 07:15 PM #21
Re: Pole Transformer
John,
The "fire box" reference was to the FPE panel, which you got.
The "fire starter" reference was to all those multiple tapped conductors being used to jump from one phase terminal to the other phase terminal - think 'double tapping is bad?, that photo shows why I use the term "multiple tap" in stead of "double tap" ... "double" means "two", and "multiple" means "more than one" and there certainly are "more than one" in those terminals.
-
11-22-2012, 07:49 PM #22
Re: Pole Transformer
Jerry
I saw quads on a breaker once, but never 7or 8 on one terminal. I was in shock. I understand it all now. Hope you had a nice Thanksgiving.
-
11-22-2012, 07:53 PM #23
Re: Pole Transformer
Raymond
Just a thought, but is this transformer at the end of a service line, and is it in the country or woods area servicing only one property?
-
11-22-2012, 10:19 PM #24
Re: Pole Transformer
Cut out switch.No doubt the property is rural, likely at least 25 km - 70 km btwn subs.Needs panel subject to higher kva ratings (25k - 150k worst case) since distribution is 3 Phase out in the sticks and for quick re-taps by POCO when they loose a phase in dist. or need to adjust during those ice storms.T to Vee.The A & C busses should have been jumped with a bar or a single rated conductor using tap lugs.
-
11-23-2012, 05:46 AM #25
Re: Pole Transformer
Yes rural property.
Pole transformer feeds three buildings.
1. House 100 amp
2. Large barn 60 amp
3. Very small studio 15'x15', no heat, just lighting and plugs, - 200 amp service
-
11-23-2012, 05:57 AM #26
Re: Pole Transformer
That is quite obviously single phase, and what about hot stick hooks like every other POCO man uses??
Personally, I think this is a setup so that the property owner can shut down power themselves to work on things. MANY farms/rural properties like this have panels ALL over the place, and there are not always disconnects.
Either a friendly utility worker set this up for them, or they went up and did it themselves. Looks very farmer to me.
-
11-23-2012, 06:14 AM #27
Re: Pole Transformer
This transformer has not been modified by the owner, it was done by the utility company/manufacture of transformer.
Each panel had a shut-off.
I found it odd that a small studio with no heat, and only light and outlet loads would have 200 amp service.