Results 1 to 8 of 8
Thread: Nec 250.32 question
-
12-05-2012, 08:35 AM #1
Nec 250.32 question
If a separate building or structure is required to have a grounding electrode Nec 250.32, why do swimming pool panels not have a separate electrode?
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-05-2012, 10:10 AM #2
Re: Nec 250.32 question
Always something to be learned here - - - I have never seen an electrical panel that could swim.
I am no pool expert, but believe they have a defacto grounding electrode via the extensive bonding of all the potential current carrying components in a pool, ( rebar, mesh, code required copper conductor grid, conductive scupper or lighting and anything requiring power ).
-
12-05-2012, 10:17 AM #3
Re: Nec 250.32 question
I see..., but under NEC: Structure: That which is built or constructed.
Such as a pool. AFA equipotential bonding, I assumed that was something different and separate.
I was just wondering about the need for a grounding electrode for separate structure. Hopefully, this isnt a stupid question, but Im sure I will find out here real quick.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-05-2012, 03:17 PM #4
-
12-05-2012, 04:09 PM #5
Re: Nec 250.32 question
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
12-05-2012, 05:51 PM #6
Re: Nec 250.32 question
The structure which holds the pool panel is typically the same structure as that which supplies the pool - the house.
The pool is a separate structure and is one giant (for concrete pools) concrete encased electrode, however, the pool is not used as such, the pool steel is bonded to the the pool perimeter bonding ring, the pool pump, the pool heat pump, etc.
The intent is that if the water in the pool becomes energized, then all things associated with the pool and within 5 feet of the pool are also energized the same as the pool water, thus no shock. While the pool is a giant concrete encased electrode, nothing has -0- resistance and any current through any resistance creates a voltage drop across that resistance, thus there could be a voltage different from ground (earth) even though the pool is one giant concrete encased electrode.
Now, taking that a step further, if the pool is a giant concrete encased electrode and IT is not -0- resistance to ground (earth), then it is easy to understand that a concrete encased electrode would have even higher resistance to ground (earth) and why a simple ground rod makes a poor grounding electrode.
-
12-06-2012, 05:13 PM #7
Re: Nec 250.32 question
Because the entirety follows strict bonding rules, including the equipotental grid, equipment, water, from the feeder source equipment grounding conductor.See Section 680, see esp.680.3, 680.6 (680.6 Number (7)), 680.21(A)(4), 680.21(B), all of 680.25 (Feeders) & 680.26 of your 2010 California Electrical Code (also IIRC, you're nearly -- if not entirely -- 100% service laterals with risers to exterior serivce equipment).
-
12-06-2012, 05:22 PM #8
Bookmarks